Electrical Panel Ground Wires - Electrical - DIY Chatroom Home Improvement Forum
Old 10-04-2012, 09:59 AM   #1
Rewards Points: 242
Electrical panel ground wires
Hello everyone. I was looking at the wiring in my fuse panel earlier and want to make sure everything is wired correctly. All the hots are separately wired and all the neutrals are hooked up separately which to me looks like, however all the grounds coming into the panel are twisted together. From there one ground wire is going to what I assume is the grounding block. The grounding block has 4 spaces with only the one being used. Is this correct? Also, if any new wiring is added can that new wire's ground go to a separate spot in the grounding block or should it just be twisted together with the rest?
Another thing i noticed is that there are two empty bars offset from the two bars that the neutral wires are connected to. I'm not sure what these are for. The shot grounding bar is tucked back in the bottom left corner of the panel.
I took a few pictures to help. The first shows all the grounds twisted together in the far back. The second shows the neutral bars, with the grounding bar in the fast back on the left. The third shows the one ground wire going to the grounding bar in the bottom left corner.
Lemkie is offline   Reply With Quote
Old 10-04-2012, 10:03 AM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 232
Not the best practice, but it has been done in many panels.
Old 10-04-2012, 10:16 AM   #3
Rewards Points: 242
What would best practice be? And also if new circuits were added should they be grounded to a separate spot on the grounding bar or just wired into the twisted group of ground wires?
Also what are the two empty bars for behind the neutral bars?
Old 10-04-2012, 10:19 AM   #4
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
No pictures.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 10-04-2012, 10:20 AM   #5
Rewards Points: 242
Originally Posted by electures View Post
No pictures.
I don't understand?
Old 10-04-2012, 10:39 AM   #6
electures's Avatar
I don't understand?
I can't see your pictures. Don't know if it is just my pc or not. Can anybody else see the pics?
Old 10-04-2012, 10:46 AM   #7
Rewards Points: 150
I see the pics just fine.
Dave632 is offline   Reply With Quote
Old 10-04-2012, 10:57 AM   #8
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
They show for me ... maybe you can see them now ?
Old 10-04-2012, 11:11 AM   #9
UAW SKILLED TRADES
Stubbie's Avatar
Best practice would be for individual grounds to be terminated separately.
Terminate the new circuit grounds separtely.
Those are just additional bars to terminate neutrals. But this also poses a question.
Is this your service equipment ... the only panel where your means to disconnect all power from the utility exists? It is necessary to know before answering some of your questions.
I'm not seeing your earth grounding or a main bonding jumper is why I'm asking.
Old 10-04-2012, 11:47 AM   #10
joed's Avatar
Rewards Points: 11,998
Two neutrals under one screw is wrong.
The grounds should be wire nutted or crimped together.
The Following User Says Thank You to joed For This Useful Post:
electures (10-07-2012)
Old 10-04-2012, 11:50 AM   #11
alexlacelle is offline   Reply With Quote
Old 10-04-2012, 11:51 AM   #12
Old 10-04-2012, 11:54 AM   #13
Rewards Points: 242
This is the only panel. I can terminate the new circuit separately on that short grounding bar. But all the others will still be twisted together with only the one wire going to the grounding bar.
Old 10-04-2012, 11:55 AM   #14
Rewards Points: 242
I did notice the two under the one screw and have room to change that.
Is there a wire nut big enough for all the wires to fit?
Old 10-04-2012, 01:31 PM   #15
UAW SKILLED TRADES
Stubbie's Avatar
Then we need to affirm your main bonding jumper. This is generally a screw or other conductive means to join (bond) the neutral bar(s) to the metal of the panel. This is critical if the grounds rely on the metal of the panel to move fault currents to the neutral bus and ultimitely the service neutral so that your fuses can open.
The Following User Says Thank You to Stubbie For This Useful Post:
mpoulton (10-04-2012)
Need to know if my grounds and neutrals are connected right dorlow Electrical 185 01-15-2012 03:54 PM
sub panel ground and neutral daddyrabbit Electrical 3 01-29-2010 07:49 AM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 10:41 PM
Bare Ground Wires MrBill_DIY Electrical 4 10-05-2008 08:05 PM
Hot Tub Install--Grounding Rod Question statgeek_rob Electrical 16 09-15-2007 03:59 AM