Electrical Panel - Ground Bar/Wiring And Safety - Electrical - DIY Chatroom Home Improvement Forum
Old 09-10-2011, 01:49 PM   #1
Rewards Points: 33
Electrical Panel - Ground Bar/Wiring and Safety
Hello,
My home has a main panel (fuses) to a distributor panel inside my home. In the distributor panel, I noticed that they put neutral and ground together in the same bus bar. I am wondering if this is ok? I have two electricians to take a look one said no, the other said yes, so I am kind of confused.
I am trying to add one or two more circuits which the current panel has some available space but ground bar is full because it is used for both ground and neutral. It's very old box (it has no GFCI nor AFCI breakers). Should I get another panel for those two new circuits and move some of the circuit there?
This panel also has open wire at the top (I mean I can see Romex out from the panel). But there is a wooden box covering the panel and those wires. Is this acceptable?
Thanks in advance,
cfreak is offline   Reply With Quote
Old 09-10-2011, 02:29 PM   #2
Code05's Avatar
Rewards Points: 1,104
Originally Posted by cfreak View Post
Hello,
Thanks in advance,
Assuming your distributer is a sub panel and is in the same building as your main, then grounds and neutrals should be separate.
Should be a 4 wire feed.
You can add ground and neutral bars.
Code05 is offline   Reply With Quote
The Following User Says Thank You to Code05 For This Useful Post:
cfreak (09-10-2011)
Old 09-10-2011, 02:41 PM   #3
Rewards Points: 33
Thanks!
My main is outside of the same building. The main panel also has neutral connected to the actual ground wire. It seems that it has only 3 wire feed. Can you recommend me what is the right way the fix this?
Old 09-10-2011, 03:12 PM   #4
Code05's Avatar
Thanks!
4 wire feed of the correct size to sub, 3 wire feed to main.
Old 09-10-2011, 03:26 PM   #5
Rewards Points: 150
Just asking because I want to know the answer; but why do you need a 4 wire feed to feed a sub?
Sunny B. is offline   Reply With Quote
Old 09-10-2011, 03:35 PM   #6
Rewards Points: 33
I think and I could be wrong.
Do you mean:
2x 120V
1x Neutral
1x Ground
I have a ground wire running from main panel (outside) passing close to the subpanel. Is it possible to use this as ground for subpanel?
Old 09-10-2011, 03:45 PM   #7
Rewards Points: 150
Do you mean:
2x 120V
1x Neutral
1x Ground
That's what my question is. Because if that is it, that isn't called a 4 wire system. It is a 3 wire system. The ground dosnt count
Old 09-10-2011, 03:58 PM   #8
Code05's Avatar
Do you mean:
2x 120V
1x Neutral
1x Ground
Yes
No
Old 09-10-2011, 04:01 PM   #9
Code05's Avatar
250.24(A)(5) Load-Side Grounding Connections. A grounded conductor
shall not be connected to normally non–currentcarrying
metal parts of equipment, to equipment grounding
conductor(s), or be reconnected to ground on the load side
of the service disconnecting means except as otherwise permitted
in this article.
Old 09-10-2011, 04:02 PM   #10
Code05's Avatar
Incorrect.
Old 09-10-2011, 04:42 PM   #11
Rewards Points: 150
Incorrect.
Are you sure. Again, just asking because I want to know. I'm confused. Isn't his house single phase, therefore 2 hots, one neutral? I thought 4 wire system was 3 hots, one neutral
Old 09-10-2011, 04:48 PM   #12
Electrician
SD515's Avatar
Rewards Points: 504
To keep the neutral and ground separate. Any equipment installed after the main service disconnect gets the neutral and ground separated. This keeps the ground from carrying current under normal situations.
Think of a typical receptacle in your home. A device plugged into that receptacle is only going to use the ‘hot’ and the neutral under normal circumstances. The ground is there to provide a low-impedance path back to the panel (actually back to the transformer via the panel) should a fault occur.
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
cfreak (09-10-2011)
Old 09-10-2011, 04:50 PM   #13
Electrician
SD515's Avatar
Rewards Points: 504
4 wire single phase feeders are 2 hots, 1 neutral, 1 ground.
3 wire single phase services are 2 hots, 1 neutral.
3 hots & 1 neutral is a 4 wire 3 phase service.
3 hots, 1 neutral, 1 ground is a 3 phase feeder.
Kyle
Old 09-10-2011, 05:17 PM   #14
Rewards Points: 150
So what about 3 wire system with ground
Old 09-10-2011, 06:56 PM   #15
Electrician
SD515's Avatar
Rewards Points: 504
A 3 wire system with ground? In what sense? As a service? Feeder or branch circuit?
No typical North American service I know of has 3 wires and ground (4 wires). Maybe 3 wires plus neutral (4 wires)=3 phase w/neutral. The utility doesn’t give you a ‘ground’ wire. They give you a grounded (neutral) wire if you need it. Most buildings do, but I have worked on a building that had 3-phase no neutral.
For services you can have 3 wires incoming, single phase=2 hots 1 neutral, or 3 phase=3 hots no neutral, or 4 wires coming in=3 phase with neutral. Making sense?
For feeders and branch circuits, 3 wire with ground can be a few different things. Could be a MWBC (2 hots 1 neutral 1 ground), an isolated ground circuit (1 hot 1 neutral 1 ‘dirty’ ground 1 ‘clean’ ground), a 3 phase circuit (3 hots 1 neutral or 3 hots 1 ground).
Kyle
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 08:40 PM
Electrical Panel "cut-in" question Todd-sta Electrical 52 12-04-2008 12:07 AM
Above Ground Pool+Deck Electrical Install (Ontario, Canada) hecubus Electrical 5 08-02-2008 02:42 PM
Hot Tub Install--Grounding Rod Question statgeek_rob Electrical 16 09-15-2007 03:59 AM
Subpanel feeder questions Silhanek Electrical 4 03-22-2007 07:30 PM