Electrical Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 07-05-2013, 02:12 AM   #1
Question
Electrical panel
I added a sub panel in my garage. I found that on the main pane,l the bus bar to the box is energized @ 120 v. The neutral bar to the box has no current. Any thought on why I'm getting power between the bus bar and the box or how to best trouble shoot?
thanks
Bill
theintruder is offline   Reply With Quote
Old 07-05-2013, 06:37 AM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
Do you mean the buss where the breakers stab into?
If so, it's because the box is bonded to the neutral (grounded conductor) in the main box.
This way, if the box comes in contact with an ungrounded conductor, it'll trip the breaker.
Therefore, no problemo
wirenut1110 is offline   Reply With Quote
Old 07-05-2013, 11:38 AM   #3
Cool
I had that sneaky suspicion after researching it last night. I wasn't 100% certain and was worried something was wired incorrectly or I had a chaffed wire. Thanks for your input, I'm feeling much more comfortable.
Old 07-05-2013, 01:40 PM   #4
Civil Engineer
Rewards Points: 4,566
Are you sure the neutral has no current? I am guessing you mean that you measured the voltage on the neutral and measured zero volts. Under load, the neutral is going to carry the difference in current between the two 120V legs in your panel. Since the legs are rarely exactly in balance, under virtually all circumstances you should measure current on the neutral, although voltage should be close to 0 (the neutral is at ground potential, which by ordinary definition is assumed to be 0 volts).
Old 07-07-2013, 05:22 PM   #5
Yes Daniel, you are correct in your assumption. When measuring voltage from neutral to the panel, I was getting 0.
Replacing an old electrical panel (w/out ground bar) yilmazma Electrical 5 12-13-2012 11:58 AM
Electrical loading question jimcorey Electrical 2 12-08-2012 08:27 AM
breaker panel positioning regulations orobono Electrical 1 10-27-2012 04:25 PM
new sub panel BlueBSH Electrical 11 01-22-2012 09:28 AM
Electrical Panel - Ground Bar/Wiring and Safety cfreak Electrical 31 09-11-2011 09:10 AM