Old 12-13-2011, 12:25 AM   #1
electrical connection for zephyr range hood.
I've installed a couple of range hoods, and they usually have a wire from the house lines. Is it acceptable to connect a range hood to a heavy duty extension cord and plug it in a regular socket? A contractor did this in one of our kitchens. This hood requires a 120 v 60 hz power supply.
darsunt is offline   Reply With Quote
Old 12-13-2011, 12:51 AM   #2
retired elect/hvac/plumb
plummen's Avatar
no
plummen is offline   Reply With Quote
Old 12-13-2011, 07:06 AM   #3
Electrician
SD515's Avatar
No, cords are for temporary use, not permanent installations.
Kyle
Old 12-13-2011, 08:34 AM   #4
HARRY304E's Avatar
Originally Posted by plummen View Post
no
Yes..
Look at 422.16 Flexible Cords(B) Specific Appliances.(4).
422.16 Flexible Cords(B) Specific Appliances (4)..
(4) Range Hoods.
Range hoods shall be permitted to be
cord-and-plug-connected with a flexible cord identified as
suitable for use on range hoods in the installation instructions
of the appliance manufacturer, where all of the following
conditions are met:
(1) The flexible cord is terminated with a grounding-type
attachment plug.
Exception: A listed range hood distinctly marked to identify
it as protected by a system of double insulation, or its
equivalent, shall not be required to be terminated with a
grounding-type attachment plug.
(2) The length of the cord is not less than 450 mm (18 in.)
and not over 900 mm (36 in.).
(3) Receptacles are located to avoid physical damage to the
flexible cord.
(4) The receptacle is accessible.
(5) The receptacle is supplied by an individual branch
circuit.
HARRY304E is offline   Reply With Quote
Old 12-13-2011, 09:10 AM   #5
A "Handy Husband"
rjniles's Avatar
422.16 says the cord used shall be a suitable appliance cord, 18 to 36" long (not an extension cord). It also says that the receptacle shall be an individual branch circuit.
The scenario the poster describes is not compliant.
Coastal South Carolina
The Following 2 Users Say Thank You to rjniles For This Useful Post:
plummen (12-13-2011), SD515 (12-13-2011)
Old 12-13-2011, 10:52 AM   #6
I can obtain an appliance cord.
What does it mean by receptacle must be on individual branch circuit?
Old 12-13-2011, 11:48 AM   #7
Electrical Contractor
A single circuit that supplies only that laod and nothing else.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 12-13-2011, 12:03 PM   #8
plummen's Avatar
Notice they say appliance cord and individual branch circuit,basically same as installing one of those built in overhead microwaves in your kitchen.
If your going to all the trouble to run a seperate circuit to mount a plug for it id just take and hard wire it on that seperate circuit myself
The Following User Says Thank You to plummen For This Useful Post:
SD515 (12-13-2011)
How to remove/replace range hood roof vent? TipsyMcStagger Roofing 2 12-08-2010 10:10 AM
Can range hood and water heater vent share same roof vent? huynh HVAC 3 09-08-2010 04:56 PM
suggestions on contructing a range hood steve1234 Carpentry 15 08-30-2010 11:35 PM
Installing a range hood NewHandyman Electrical 1 08-10-2009 10:42 AM
Range hood, hardwire or receptacle? DIYGST Electrical 11 01-10-2009 07:55 AM