Hello I am in the process of finishing my basement. I have installed new circuits in panels before with no issues to speak off. My plan was to add 3 new circuits, 1 for lights, 1 for plugs and 1 for bar area.
Upon opening my box I have noticed something that concerns me.
I have no more available slots in the grounding bars to add a circuit yet there is 6 empty slots open in the panel. It looks like there is room to add another bar though on both sides. Is this possible?
1. All Neutral and Ground wires are screwed to same bars on both sides of the box. Does this matter?
2. I have no more available slots in the grounding bars... It looks like there is room to add another bar though
Equipment grounding conductors can be doubled or tripled under one screw per manufacturers installation instructions. Neutral conductors can only be one wire per terminal. You may have to do some re-arranging. Be sure to turn off the panel before working on it.
Ok well that should solve my issue. I really only need 2 slots so only 2 ground wires would be doubled. I had considered adding a bar but wasn't really sure what that involved.
It'd be nice if I had 125A or 200A service instead of only 100A, but since there are plenty of spaces this should be no issue correct?
Also when adding circuit for wetbar area would include some small lighting, a few receptacles and fridge. Does this need to be a 20A circuit?
As mentioned if you do move around neutral close the MAIN. If your going to add another bar: if it will only be used for grounds the attaching it to the panel enclosure with threaded screws that engage at least 2 threads will be fine. However if you wish to terminate neutrals there as well, you must run a jumper of sufficient size between the two ground/neutral bars.
That depends on who you ask and where you live. This type of breaker is supposed to suppress any arcing that may happen and reduce the fire hazard associated with it. Some communities were trying to make it code in Indiana and I don't know whether or not they ever did. Frankly, what good is it to have only one? If the rest of your breakers are not AFCI then don't waste your money on just one.
If the receptacle is within 6" of the sink, it has to be GFCI protected.
I am sure you meant 6' ( 6 feet).