Electrical - Electrical - DIY Chatroom Home Improvement Forum
Old 12-18-2010, 10:55 AM   #1
Electrical
I have a dryer hook up with a 30amp breaker on about 28 ft of 10-2 with ground (Orange wire). I have tested all componenets and it will not start the dryer under load? It stains to start. Must it be 10-3 with ground or do I need to go to 8 ga.
RJCIII is offline   Reply With Quote
Old 12-18-2010, 11:00 AM   #2
Electrical Contractor
kbsparky's Avatar
A new dryer circuit would need a 10/3 w/ground in it, and a 4-prong cord and receptacle.
The motor uses 120 Volts to operate, and without the proper configuration and connections it won't work properly.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
RJCIII (12-18-2010)
Old 12-18-2010, 11:10 AM   #3
Also need to make sure the 10/3 +G is properly connected to a 30A double-pole breaker with tie-bar. Can't tell from the OP if the correct breaker was used.
clashley is offline   Reply With Quote
Old 12-18-2010, 11:15 AM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,948
Both previous replies are dead on.
10/2 IS NOT legal or safe to use for this 120/240v circuit. You are using a bare ground wire as the neutral as it stands. This is a big problem.
You DO need 10/3 and a 4-wire receptacle.
The problem with the dryer running is most likely that you installed the breaker wrong. I suspect it is an FPE or GE skinny breaker. Am I right?
Speedy Petey is online now   Reply With Quote
Old 12-18-2010, 07:51 PM   #5
Dryer Hook up
The 10-2 wire has the bare grounding wire hooked up to the grounding bar in the breaker box. I though it might need to be hooked to the neutral bar? Also the receptical is an three prong stove receptical. So it looks like a mess and I need another 10 gage wire in the mix, a four prong dryer receptical, dryer cord and try fishing a single wire back to the breaker box - thanks
Old 12-18-2010, 08:00 PM   #6
Mad Scientist
No dice, you can't just run another separate wire alongside the cable. You need to replace the cable with the proper 10-3 w/ground. You need to replace the receptacle with the proper 4-prong, and replace the dryer cord with a 4-prong.
McSteve is offline   Reply With Quote
The Following User Says Thank You to McSteve For This Useful Post:
Speedy Petey (12-18-2010)
Electrical Questions from a Foreigner mark_anderson_u Electrical 4 09-10-2010 06:46 AM
Changing from Electrical Cook Top to Electrical Range EkS Electrical 24 06-22-2010 10:43 AM
How to install new electrical box without attic access gilmores33 Electrical 10 02-14-2010 07:46 PM
Slight electrical current in bathroom faucet water + other unusual electrical events story Electrical 9 09-16-2009 10:28 PM
Electrical box replace,addiitions, city permits and looking for an electrician ramchy Electrical 3 08-02-2009 11:12 AM