Old 06-21-2011, 03:34 PM   #1
Unhappy
electrical
hello, I need to now how to wire my compressor? Its a 5hp 230v 15amps 60 1 phaze compressor, I have 12/3 wire for it and its located about 5ft from panel, I have a 220 outlet in my laundry rm we dont use, so i have located the breaker for it and was planning on using those breakers for my compressor,which is a 30amp pole breakers, i just need to know which wires goes to the breaker and to my switch on compressor, the 12/3 has a red,blk,white, bare copper wire for ground,I just need to know where these wires go on the switch of compressor,and inthe panel??? the 220 outlet is wired in panel to the breaker as follows, red,blk to 30amp pole breaker,and white wire to the ground,with no bare copper wire.? i would appericate the help with this ..
Thanks Johnx
johnx is offline   Reply With Quote
Old 06-21-2011, 04:03 PM   #2
Lic Electrical Inspector
electures's Avatar
electrical
Thanks Johnx
#12 is not large enough. Neither is the 30A breaker. You will need #8 copper with a 70A breaker.
All responses based on the 2011 NEC.
If you live in New Jersey click
. All other states click
Please check with local, county and state officials as laws may vary.
Sizing motors
. Online motor calculator
. Online calculators
electures is offline   Reply With Quote
Old 06-21-2011, 04:46 PM   #3
A "Handy Husband"
rjniles's Avatar
electrical
Do not understand this #8 with 70 amp breaker. 5 HP is 3730 watts. At 240 volts that is a little over 15 amps. 12-2 with a 20 amp 2 pole breaker should be fine.
To the OP, if the compressor is labeled 240 VAC and not 120/240 VAC, you do not need a neutral connection. Only the 2 hots need be connected to the 2 pole breaker.
Coastal South Carolina
The Following User Says Thank You to rjniles For This Useful Post:
del schisler (06-22-2011)
Old 06-21-2011, 05:24 PM   #4
just a tool guy
mickey cassiba's Avatar
electrical
P'raps I missed something, but why on earth would a 15 amp machine require a 70 amp breaker?
Mickey
One of these hammers will fix it.
mickey cassiba is offline   Reply With Quote
Old 06-21-2011, 09:03 PM   #5
electures's Avatar
electrical
The nameplate FLA (full load current) is not used for sizing branch circuit conductors or the OCPD. The following is the procedure to be followed for a 5HP, 240V single phase motor.
430.6(A) 1 states;
(1) Table Values. Other than for motors built for low speeds (less than 1200 RPM) or high torques, and for multispeed motors, the values given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250 shall be used to determine the ampacity of conductors or ampere ratings of switches, branch-circuit short-circuit and ground-fault protection, instead of the actual current rating marked on the motor nameplate. Where a motor is marked in amperes, but not horsepower, the horsepower rating shall be assumed to be that corresponding to the value given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250, interpolated if necessary. Motors built for low speeds (less than 1200 RPM) or high torques may have higher full-load currents, and multispeed motors will have full-load current varying with speed, in which case the nameplate current ratings shall be used.
Table 430.248 indicates 28 amps for a 230V 5HP single phase motor.
430.22(A) General states;
(A) General. Conductors that supply a single motor used in a continuous duty application shall have an ampacity of
not less than 125 percent of the motor’s full-load current rating as determined by 430.6(A)(1).
28A x 125% = 35A
Table 310.16 indicates #8AWG is rate for 40A.
Next we look at sizing the ground fault, short circuit, overcurrent protective device.
430.52 states;
430.52 Rating or Setting for Individual Motor Circuit.
(A) General. The motor branch-circuit short-circuit and ground-fault protective device shall comply with 430.52(B) and either 430.52(C) or (D), as applicable.
(C) Rating or Setting.
(1) In Accordance with Table 430.52. A protective device that has a rating or setting not exceeding the value calculated according to the values given in Table 430.52 shall be used. (Also read the exception.)
Table 430.52 states that for an inverse time circuit breaker protecting a single phase motor it is to be sized at 250% of the FLA as stated in Table 430.248.
28A x 250% = 70A
Based on the above calculation a 70A ITCB is correct.
If the motor fails to start and run then 430.52(C) (1) Exception No. 2(c) can be applied which states;
(c) The rating of an inverse time circuit breaker shall be permitted to be increased but shall in no case exceed 400 percent for full-load currents of 100 amperes or less or 300 percent for full-load currents greater than 100 amperes.
28A x 400% = 112A
Since we can’t exceed 400% of the motor FLA we round down to a 110A ITCB on a piece of #8 AWG conductor.
Sizing motors
Old 06-21-2011, 09:06 PM   #6
electures's Avatar
electrical
Sorry but that is not how it is done. Please see above post.
Sizing motors
Old 06-21-2011, 09:36 PM   #7
Electrician
SD515's Avatar
electrical
430.52 states;
I read it as Tbl 430.52 allows a maximum up to 250%, not that it has to be rated @ 250%, otherwise I agree with what you said.
Kyle
Old 06-21-2011, 09:54 PM   #8
Missouri Bound's Avatar
electrical
You would be best to use a 30 amp breaker with #10 wire for that compressor. How is the compressor controlled? Does it just have a pressure switch? Any information on the compressor would be helpful....a picture would be great. We have run a 5 HP single phase compressor for nearly 9 years now with a 30 amp breaker and 10 ga wire. It's most likely you will need only 2 wires to the compressor, one for each hot leg. You will just need to tape the end of the conductor (white) with black tape to indicate it is a hot wire. Would you just consider running a whip from the panel to the compressor instead of your romex? It makes for a neater installation and you could pull two black or red wires instead of marking the cable.
Old 06-21-2011, 11:21 PM   #9
electures's Avatar
electrical
Look at the end of the sentence. "shall be used".
Sizing motors
Old 06-21-2011, 11:25 PM   #10
electures's Avatar
electrical
I quoted exactly what the code requires. Anything less is unsafe. Just because your compressor is wired wrong is not justification for wiring another one illegally. It requires #8 wire and a 70A breaker.
Sizing motors
Old 06-21-2011, 11:31 PM   #11
electrical
Two things. Electures just pointed out that SD515 is correct....and I'm wondering if electures has any practical experience wiring motor circuits? The nec is difficult to understand for many, so I understand if that is the interpretation problem. But overprotection is the best way to destroy a motor. This isn't that complicated. A motor with a FLA of 15 amps can be protected at 125% of that, which is 18.75 (or 20 amp). A simple look at the owners manual of any compressor will validate this.
Old 06-21-2011, 11:37 PM   #12
Electrical Contractor
electrical
What do you want to bet that it is not a true 5hp motor.
If this is a compressor from the box store, I am sure it is not a 5 hp motor.
If the instructions say to use a 20 amp breaker, there you go.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 06-21-2011, 11:41 PM   #13
electures's Avatar
electrical
SD515 is incorrect. 35 years wiring motors and controls. 21 years teaching it to electricians, contractors and inspectors. The 70A breaker has nothing to do with protecting the motor. It protects the branch circuit conductors (which is why it is called motor branch circuit protective device). The motor itself is protected by the overload device.
Sizing motors
Old 06-21-2011, 11:42 PM   #14
electrical
jbfan...very good point. They often use the term "develops 5 hp" which is a clever way to advertise.
Old 06-21-2011, 11:48 PM   #15
electures's Avatar
electrical
I bet you are correct. Wonder what the nameplate reads.
Sizing motors
DIY Electrical work in New Jersey electures Electrical 42 12-19-2012 04:19 PM
Electrical Questions from a Foreigner mark_anderson_u Electrical 4 09-10-2010 07:46 AM
Changing from Electrical Cook Top to Electrical Range EkS Electrical 24 06-22-2010 11:43 AM
How to install new electrical box without attic access gilmores33 Electrical 10 02-14-2010 08:46 PM
Electrical box replace,addiitions, city permits and looking for an electrician ramchy Electrical 3 08-02-2009 12:12 PM