Richo 03-13-2009 02:14 PM
I am looking to install 2 1500W 240V electric heaters in a basement. I'm going to use 12 gauge wire for each heater but here's my question:
I'm aware that 12 gauge is good for up to 20 amps @ 120V but if you are using 240V, does that mean you can go up to 40 amps and run both of these heaters off the same circuit/wire? And if so, would I use a 40 amp double pole breaker?
If they need to be run on separate circuits, do I just need a 20 amp double pole breaker for each heater or 40 amp?
Thanks for your help.
47_47 03-13-2009 02:25 PM
12 gauge is good for 20 amps.
1500W/240V= 6.25 A each
Use 12-2, put them on one circuit with a double pole 20.
Just make sure your thermostat can handle the wattage.
Richo 03-13-2009 02:41 PM
Thanks! I was hoping that I could save on extra length of wire and an extra breaker. I appreciate your help!
47_47 03-13-2009 02:56 PM
Just to be complete, 12 gauge is good for 20A, 80% continous (16A). Your total amperage is 12.5 and you can put 16 on this circuit. Do these heaters have an internal thermostat? If they don't I recommend running your wire to the first stat and pigtail it to a second stat. This way you can operate the heaters independantly.
InPhase277 03-13-2009 06:58 PM
You have been given good advice already, so I'll just clarify a little theory for you. Amps heat a conductor the same regardless of the volts. A #12 conductor is good for 20 amps period, 12 V, 30 V, 120 V, 600 V.
Richo 03-13-2009 08:50 PM
Each heater will be controlled by its own line voltage thermostat so I will want them to run independent of each other.
I had a simple electrical class many years ago and learned about Ohms law, etc...just had been a while so I wanted to make sure I had it right before I proceeded.
Thanks for your great advice.