txrun 12-23-2009 10:39 AM
I have a 6 year old house that has an island cooktop. It was wired for an electric cooktop (4 wire 240V with a 40 amp breaker). However, a gas range was installed in the house when we bought it.
I just noticed that in the cabinet underneath the gas cooktop, we have two 20 amp receptacles. One is for the gas range and the other is on the end of the island for general use. The electrician who wired the house took one of the hot wires from the 240 circuit for one of the 120V receptacles and the other hot for the second 120V receptacle. Wiring to the recepticles themselves are 12 gauge.
Problem is, I still have a 40 amp breaker in the panel protecting all of this.
I am guessing I need to replace the 40 amp breaker with two 20 amp breakers in the panel but I'd like some thoughts from people who know more than I do.
I appreciate any help.
joed 12-23-2009 11:00 AM
Yes you abolutley need to replace that breaker with 20 amps. If the receptacle is present for the stove it should be removed also.
electures 12-23-2009 12:37 PM
Originally Posted by txrun (Post 371169)
i have a 6 year old house that has an island cooktop. It was wired for an electric cooktop (4 wire 240v with a 40 amp breaker). However, a gas range was installed in the house when we bought it.
I just noticed that in the cabinet underneath the gas cooktop, we have two 20 amp receptacles. One is for the gas range and the other is on the end of the island for general use. The electrician who wired the house took one of the hot wires from the 240 circuit for one of the 120v receptacles and the other hot for the second 120v receptacle. Wiring to the recepticles themselves are 12 gauge.
Problem is, i still have a 40 amp breaker in the panel protecting all of this.
I am guessing i need to replace the 40 amp breaker with two 20 amp breakers in the panel but i'd like some thoughts from people who know more than i do.
#12 = 20a
220/221 12-23-2009 09:25 PM
1. Double check the neutral (white wire) connections where he tied into the original 240V circuit and make sure they are absolutely tight.
2. Install a 2 pole 20 amp breaker to replace the 2 pole 40.