Originally Posted by Speedy Petey View Post
PLEASE stop giving electrical advice. You are obviously not a professional and really don't know what you are talking about.
Code05 is offline   Reply With Quote
The Following User Says Thank You to Code05 For This Useful Post:
Speedy Petey (11-01-2011)
Old 11-01-2011, 08:25 PM   #17
Code05's Avatar
THIS is your answer.
DO NOT change the receptacle, unless you are 100% certain you have a ground conductor as well as the required neutral. Four wires total.
I agree.
Remember to reattach bonding strap in the dryer.
Old 11-01-2011, 08:30 PM   #18
I'm Your Huckleberry
Rewards Points: 2,270
Originally Posted by DexterII View Post
The store where you bought the dryer, or any hardware store or big box will have the cord that you need.
I bought them from my father's lady friend. They're almost two years old, still under warranty though. Thanks bud but what's the final conclusion, change to a three wire cord, dropping the ground internally from appliance I'd presume, or change the receptacle and not use the non existing ground?
I'm most definitely not helping the landlord out and pulling in a new wire so something is going to be missing regardless.
Doc Holliday is offline   Reply With Quote
Old 11-01-2011, 08:37 PM   #19
Code05's Avatar
CORD and reattach bonding strap. This is specifically allowed in 250.140.
250.140 Frames of Ranges and Clothes Dryers. Frames
of electric ranges, wall-mounted ovens, counter-mounted
cooking units, clothes dryers, and outlet or junction boxes
that are part of the circuit for these appliances shall be
connected to the equipment grounding conductor in the
manner specified by 250.134 or 250.138.
Exception: For existing branch-circuit installations only
where an equipment grounding conductor is not present in
the outlet or junction box, the frames of electric ranges,
wall-mounted ovens, counter-mounted cooking units,
clothes dryers, and outlet or junction boxes that are part of
the circuit for these appliances shall be permitted to be
connected to the grounded circuit conductor if all the following
conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire;
or 208Y/120-volt derived from a 3-phase, 4-wire, wyeconnected
system.
(2) The grounded conductor is not smaller than 10 AWG
copper or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded
conductor is uninsulated and part of a Type SE serviceentrance
cable and the branch circuit originates at the
service equipment.
(4) Grounding contacts of receptacles furnished as part of
the equipment are bonded to the equipment.
The Following 2 Users Say Thank You to Code05 For This Useful Post:
DexterII (11-01-2011), Doc Holliday (11-01-2011)
Old 11-01-2011, 08:49 PM   #20
Rewards Points: 22
Agreed. I should have been more clear when I initially said to change the cord, but now you have the facts.
The Following User Says Thank You to DexterII For This Useful Post:
Code05 (11-01-2011)
Old 11-01-2011, 08:58 PM   #21
I just talked to my bud, he said the same thing. Change the cord and attach the bonding strap, ground to neutral.
Said it's not legal but it's *acceptable to change the receptacle and bond it in there, same difference.
*cheaper.
Told me best to change the cord and keep in compliance which is what I'll do.
Thanks everyone for the help.
Old 11-02-2011, 07:35 AM   #22
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,034
It is not acceptable to change a properly wired dryer receptacle (3 or 4 wire) to match a dryer cord. Changing the dryer cord to match the receptacle is the only compliant option. Because it is cheaper is not an option.
Since you indicate you are changing the cord you have selected the correct (and compliant) method.
Coastal South Carolina
rjniles is offline   Reply With Quote
The Following User Says Thank You to rjniles For This Useful Post:
Code05 (11-02-2011)
Old 11-02-2011, 10:45 AM   #23
You didn't catch the "cheaper" bit. First and foremost my friend has been working as a full time electrician since the age of 16. He's been studying since the age of 17. Journeyman in his mid 20's, master by 29. Booming electrical business owner and operator by 30, been running that business for 5 years now. He got back yesterday from a week in Salt lake City and is now a certified lighting specialist and programmer of some sort, successfully brightening if you will, his knowedge and expansion of his company.
There is not an electrician's opinion on the face of this planet I trust more. If in his opinion wiring a hot to a ground is acceptable than it is.
He wouldnt' say "it's ILLEGAL" if it were not either. Thanks though.
Old 11-02-2011, 10:56 AM   #24
You also missed where I said "best friend."
Old 11-02-2011, 02:35 PM   #25
A "Handy Husband"
rjniles's Avatar
Your best friend is still giving you a bum steer
Code05 (11-02-2011)
Old 11-02-2011, 02:44 PM   #26
Licensed electrician
Rewards Points: 1,010
You friend is wrong. You do not install a 4 wire receptacle on a 3 wire system. As you have been told by several the correct method is to change the cord to a 3 wire cord and add the bond jumper on the dryer.
Code05 (11-02-2011)
Old 11-02-2011, 04:49 PM   #27
Someone stab me in eyes with a dull pitchfork now, please.
Old 11-02-2011, 04:58 PM   #28
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
Friends are some of the worst places to get electrical advice.
Old 11-02-2011, 05:30 PM   #29
Maybe in your experience, not mine. You need better friends.
Has no one comprehended where it was stated that it was illegal. The only difference is where the bond would be, in the appliance or in the receptacle and the latter being illegal but would work the same. Not only in theory but in actuality but there's a reason for bonding in the receptacle being illegal.
The bit about him saying to change the cord and keep it compliant to NEC went right in one eye and out the other, huh?
Good grief.
Old 11-02-2011, 05:44 PM   #30
I didn't me mean silly. I don't need friends to give me electrical advice.
electric outlet rafa7 Electrical 0 04-22-2011 08:07 AM
Covering an electric outlet with cabinets Georgejc Electrical 15 04-20-2011 11:52 PM
90 amp electric car charger! The future... Billy_Bob Electrical 16 02-16-2010 03:01 PM
help! with electric outlet Brad325 Electrical 7 05-03-2009 12:01 AM
Wiring a switch, power from outlet Big Bill Electrical 4 09-15-2007 04:59 PM