Electric Cooktop Wiring Issues - Electrical - DIY Chatroom Home Improvement Forum
Old 04-13-2012, 01:13 AM   #1
Electric cooktop wiring issues
I bought a frigidaire cooktop, electric. It was a display model and didn't have the instructions. I believe I found the correct manual online ( http://www.aimtofind.com/files/FGEC3045KB-4.PDF ) but here is my problem....
The whip looks like number 8 or number 10 cable, there is only 3 wires total...
The manual doesn't specify what gauge wire to supply the junction box the whip will connect to. Secondly I know it needs to
Be a 240v circuit with 40 amps but how do I do this if I only have three wires on the cooktop itself?
So my question is... What gauge wire to run to the panel and how do I make those connections if going from a 2 wire cable to a three wire cable?
kbrookst is offline   Reply With Quote
Old 04-13-2012, 01:21 AM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If you are running romex, you need to run 8-2. This is a 240V appliance, not a 120/240V appliance, so you do not need a neutral. You will have 2 hots and a ground. Just make sure to tape the white wire with black tape.
If you have to run a new circuit for the cooktop, I would suggest running a 8-3 romex, use the black and the red for your hots (bare for ground) and cap off the neutral in the JBox. That way, if you ever need it in the future, you don't have to rerun the circuit because you don't have a neutral.
Old 04-13-2012, 01:21 AM   #3
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
8 gauge wire. If only three wires are needed then you just need three wires to feed it.
Personally if this is where a normal range can go I like to feed any range in a home with 6-3 so there is always rhe option a normal range can be used.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 04-13-2012, 01:24 AM   #4
k_buz's Avatar
Why 6-3? A typical range only needs a 40A circuit? or do you use 6-3 SER?
The Following User Says Thank You to k_buz For This Useful Post:
Speedy Petey (04-13-2012)
Old 04-13-2012, 01:34 AM   #5
rrolleston's Avatar
6-3 CU NM wire every full size range I have had to install is put on a 50 amp circuit unless and exception is an wall over or cooktop.
Old 04-13-2012, 01:37 AM   #6
k_buz's Avatar
8 CU is rated to 50 Amps
Old 04-13-2012, 04:52 AM   #7
kbsparky's Avatar
While this is true if one were to install type THHN wire in a conduit, #8 type NM cable is limited to 40 Amps....
-KB
Old 04-13-2012, 06:45 AM   #8
k_buz's Avatar
Why would that be?
Old 04-13-2012, 06:51 AM   #9
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
A full size range, rated 12kW or less, can be on a 40A circuit, wired with #8, and with a 50A receptacle.
You DO NOT need #6 unless the range is 12.1kW or more.
Speedy Petey is online now   Reply With Quote
Old 04-13-2012, 06:52 AM   #10
#8NM cable is rated for 40A.
#8THHN in conduit is rated for 50A.
NM cable MUST use the 60deg C column.
THHN can use the 75deg C column for new circuits.
Old 04-13-2012, 06:58 AM   #11
k_buz's Avatar
Makes me second guess just about everything I thought I knew.
Old 04-13-2012, 10:31 AM   #12
Code05's Avatar
Rewards Points: 1,104
Good, it will make you a better sparky. I have many of my mis-conceptions corrected and I am thankful for it.
Code05 is offline   Reply With Quote
The Following User Says Thank You to Code05 For This Useful Post:
Old 04-13-2012, 11:00 AM   #13
rrolleston's Avatar
Got used to running 6-3 in new construction as a rule because we were not sure what would be used. That covers many options in the future.
Old 04-13-2012, 11:54 AM   #14
to clarify, THHN can use the 75 degree C column PROVIDED all the terminations are also rated 75 degree C. the circuit breaker terminals may be rated 75 degree C but i'm not sure about the cooktop. as the cooktop is less than 100A, you would need to use the 60 degree C ampacity values if the terminal temp rating of the cooktop and/or circuit breaker cannot be determined.
itsnotrequired is offline   Reply With Quote
Old 04-13-2012, 12:12 PM   #15
jbfan's Avatar
Rewards Points: 140
To throw another thought out there.
What if the cook top came with a preinstalled whip, and you never touched the terminals?
Also what if you wired to a receptacle?
Would you use the 75 degree colunm for thwn?
wiring electric cooktop 4 wires to 3 wires 1234mom Electrical 34 07-02-2011 07:12 AM
Pool pump, cleaner, light wiring issues tulsajeep Electrical 4 06-05-2011 07:56 PM
wiring in new cooktop yamaman Electrical 23 11-06-2010 06:32 PM
wiring 110 instead of 220 electric water heater Master Brian Electrical 14 08-22-2010 05:06 AM
Wiring from electric motor subman Electrical 1 06-24-2005 11:37 PM