Ele Hot Water Tank And Welder Sharing Circuit - Electrical - Page 3 - DIY Chatroom Home Improvement Forum
Old 03-18-2008, 06:59 PM   #31
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Great a picture. Well it's a a cutler hammer ch it looks like. My first guess is that it should have a backfed double pole breaker as a main.. It would be nice to see it with the front cover removed but don't do this if you are uncomfortable with that.
Maybe others will chime in.
Old 03-18-2008, 07:11 PM   #32
He named the five double poles that are in that outside panel and the largest was the 60A for the sub panel. No main???
jerryh3 is offline   Reply With Quote
Old 03-18-2008, 07:15 PM   #33
UAW SKILLED TRADES
Stubbie's Avatar
Yep no main if he is correct. The sub has no main but that's ok the outside panel must have a main unless it is split bus. It is possible someone hung a main lug panel for the service equipment if so this needs to be corrected. This is not a meter main so I'm inclined to think this was done after the fact.
Old 03-18-2008, 07:37 PM   #34
What kind of welder is it and how many prongs are on the plug. I have 3 welders and they can't use the same recepticle, or feed.
RobertS is offline   Reply With Quote
Old 03-18-2008, 07:43 PM   #35
it's a lincoln and 4 prongs
inside pic
wazeaz is offline   Reply With Quote
Old 03-18-2008, 07:46 PM   #36
what is a "main lug panel"
Old 03-18-2008, 07:51 PM   #37
You have a main lug panel. It's a panel where the main connections go right down to the bus bars without a main breaker.
Old 03-18-2008, 08:11 PM   #38
UAW SKILLED TRADES
Stubbie's Avatar
Wazeaz
Before I comment could you take a good picture of the area just below the breakers I'm not seeing any bus stabs.
Old 03-18-2008, 08:12 PM   #39
It is a 3 pole 4 wire grounding plug. Forget the hot water heater idea. Unless your hot water heater is 4 wired.
Old 03-18-2008, 08:25 PM   #40
Wazeaz
pics.............
Ele hot water tank and welder sharing circuit-0318082019b.jpg   Ele hot water tank and welder sharing circuit-0318082019.jpg
Old 03-18-2008, 08:59 PM   #41
UAW SKILLED TRADES
Stubbie's Avatar
Ok you have a real big mess going on. This appears to be a modified panel board where the guts from another panel have been installed and the busses shortened by either cutting or some other method. And I'm not sure that isn't a jury rigged 3 phase bus insert. You must have a main and you don't.
At this point I think you need to call in an electrician to advise you.
Also if you have a 4 prong plug as Robert has mentioned either your welder is not 240 volts only or someone has the wrong cord or plug installed on it. If it does require a 4 prong plug then the water heater idea is out the window.
I'm sorry this went South so to speak but you have got a lot of issues to take care of and you need to get a pro in to fix it.
I've never seen anything like what you have there.
Old 03-18-2008, 09:18 PM   #42
Electrical Contractor
jbfan's Avatar
Rewards Points: 224
I have seen some CH that did not have buss bars the entire lenght of the panel, but never that short. Most have been 2 slots.
Where do you turn off that panel from?
Old 03-18-2008, 09:27 PM   #43
UAW SKILLED TRADES
Stubbie's Avatar
JBfan
There is no main and it isn't split bus so I'm not real sure what the heck he has there.
Old 03-18-2008, 10:05 PM   #44
" Euro " electrician
frenchelectrican's Avatar
Dangbat this is the most unuseal box i did see that for a quite a while.
however i dont know if you can find the breaker box number somewhere but i did look at my catalog to verify it and can you run the number by me ??
according to my catalog book it say CH12L200R that is a 12 space main lug outdoor verison unless someone swap the gut in there.
Merci, Marc
However but if the OP have under 6 throw total on that breaker box then it dont need a main breaker.
Last edited by frenchelectrican; 03-18-2008 at 10:07 PM. Reason: add info about the 6 throw rule
Old 03-18-2008, 11:02 PM   #45
UAW SKILLED TRADES
Stubbie's Avatar
Well I didn't give the 6 throw rule a chance I guess but that makes sense in this case. Still it doesn't look right to me. Unless I'm blind it appears to be cut off to limit the # of breakers and I am sure the electrician was using the 6 throw idea when he did this. It works but to me it is a hack. Anyway thanks for getting my ship pointed back in the right direction.
I've never seen a panel with 12 spaces with that much unused area but I guess that must be the case. It still looks to me like somebody whacked off the bus assembly insert. I do notice that the service entrance looks newer. Why all the unused blank breaker knockouts in the cover? I'm more inclined to think it is a 30 space panel and the guy whacked off the busses.