Old 10-30-2008, 10:24 PM   #16
Originally Posted by Speedy Petey View Post
W - T - F does this have to do with ANYTHING?????
Means the OP is very likely not to hurt himself.
Speaking of WTF, do you realize that you are allowing my post to control your blood pressure?
Are you OK with that?
Old 10-30-2008, 10:50 PM   #17
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
After your advice? His chances just skyrocketed.
Please. Don't flatter yourself. You have NO effect on my BP, I assure you.
Speedy Petey is online now   Reply With Quote
Old 10-31-2008, 08:14 AM   #18
Yes, if your ohmmeter can read fractions of an ohm.
If you have #12AWG and you read 1.5 ohms, your dead short is 25' from the breaker, assuming the short doesn't change when 120v is not applied. With #14 the short is 30' from the breaker.
Exactly, and it can help us estimate the distance, much better than risking your life...or your eyes.
rgsgww is offline   Reply With Quote
Old 10-31-2008, 12:36 PM   #19
I think my distance numbers are wrong; it's 0.16 ohms for 100' (loop distance) of #12.
That's why you need to pass heavier current to trace short circuits and measure the voltage drop. A 100w bulb will pass ~0.8A, then R = E/I. This short at the end of 50' of Romex would read 0.13V.
The other way is TDR, but that's out of the DIY league.