Hello,
I am redoing my electrical system from the weatherhead to the breaker box so I'm sure I'll be asking quite a few questions in the relatively near future.
My city uses the 2008 NEC with virtually no amendments (none pertaining to what I'm doing).
I've got a copy of the NEC... wow, what a document, HA!
I've got the permit already and have been in contact with the inspector already.
He says my best bet is to use 2 grounding rods (so he doesn't have to measure resistance in the soil etc if I only have one).
What size (diameter) solid copper rods are used?
What length?
When they are placed 6' apart, is that: no more than 6, no less than 6, or exactly 6'?
Thank you all for your help!
Flooring Installer. Ecological Restoration Technician. Green Building Enthusiast. Obsessed with insulating and air sealing.
wewantutopia is offline   Reply With Quote
Old 08-07-2012, 10:55 PM   #2
Electrical Contractor
kbsparky's Avatar
Copper ground rods have to be a minimum " in diameter, 8 feet long.
You can get 3/4" rods that are 10 feet long, if you prefer.
The 6 foot spacing is a minimum, and if you can space them further apart, they will be more effective.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
MisterZ (08-07-2012)
Old 08-07-2012, 11:41 PM   #3
"So I Re-Wired It"
MisterZ's Avatar
just be sure to run the ground wire from the panel to each rod and back to the panel again.
Knowledge is Power, but 240v can Keel You!!
MisterZ is offline   Reply With Quote
Old 08-08-2012, 04:30 AM   #4
kbsparky's Avatar
There is no basis for such a requirement in the NEC.
Only one lead is required to be connected to the panel, and that single lead can loop from rod to rod and end at the farthest one.
IF the grounding electrode conductor is cut at the first rod, a second clamp would be required for the jumper to the next rod in most cases.
-KB
The Following 4 Users Say Thank You to kbsparky For This Useful Post:
electures (08-08-2012), MisterZ (08-08-2012), Speedy Petey (08-08-2012), stickboy1375 (08-08-2012)
Old 08-08-2012, 04:48 AM   #5
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
I'm not sure if this may have changed in '08 or '11 but, I always thought it had to be continuous unless of course it was by irreversible connection?
wirenut1110 is offline   Reply With Quote
Old 08-08-2012, 05:23 AM   #6
kbsparky's Avatar
Continuous until you terminate at the first rod.
Note the multiple clamps on the rods in this graphic:
-KB
The Following 2 Users Say Thank You to kbsparky For This Useful Post:
Speedy Petey (08-08-2012), wirenut1110 (08-08-2012)
Old 08-08-2012, 05:36 AM   #7
Rewards Points: 510
Guess I've been saving money using less clamps..
Old 08-08-2012, 06:25 AM   #8
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,990
There are also 5/8"x8' clad or galv rods.
Old 08-08-2012, 06:26 AM   #9
This is a very common misconception. The wire from the panel to the first rod is the GEC. The wire between the two rods is a bonding jumper.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Old 08-08-2012, 07:52 AM   #10
Rewards Points: 181
Wow, thanks for all the replies!
How deep should the ground wire connecting the rods be?
What gauge wire?
Old 08-08-2012, 08:52 AM   #11
"So I Re-Wired It"
MisterZ's Avatar
I use #6 Cu grounding wire.
Kb and Petey, thank you for clearing that up. I have never seen any such code either, but the inspector i use asks for this ground loop.
Never questioned it. Just figured he was the one passing my work
Old 08-08-2012, 09:27 AM   #12
Rewards Points: 79
I just went through this grounding and NEC2011 for my electrical permit in CO. I could not have succeded without the book and my electrician friend.
My building site is on a granite mountain. We tried, but could not pound the grounding rod far enough into the ground. I had the excavator dig a trench near my sub panel. Since it is a sub panel, I only need one grounding rod.
Before I bought the property, it had a house that burned down. The garage is still standing (150ft from the former house and transformer), but no electricity. My permits are to connect the garage and begin the process for a new house.
When the inspector came to inspect the trench and grounding we discussed a bit about the future house. He mentioned a Ufer grounding system. NEC has nothing about this, but I did find some details on line. Does anyone here know about Ufer?
gobug is offline   Reply With Quote
Old 08-08-2012, 09:40 AM   #13
Licensed electrician
Rewards Points: 1,872
A Ufer is called a concrete encased electrode in the code.
Old 08-08-2012, 10:19 AM   #14
Rewards Points: 79
Thanks Jim
I found it. p239
Old 08-08-2012, 11:06 AM   #15
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Please explain.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Grounding Switches.... stickboy1375 Electrical 3 08-03-2012 06:59 AM
Need to know if my grounds and neutrals are connected right dorlow Electrical 185 01-15-2012 02:54 PM
Fried electronics after earth ground accidentally disconnected oukachiru Electrical 7 07-12-2011 03:05 PM
NEC Question Jafsvcs Electrical 1 06-13-2007 05:45 PM
3 phase anyone? Tomkah Electrical 3 01-05-2007 05:18 PM