Driving Wire Through Buried Conduit - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 07-06-2009, 03:07 PM   #16
Rewards Points: 1,062
so will someone actually say if buried conduit is actually a wet or dry location ?
Old 07-06-2009, 03:09 PM   #17
General Contractor
MacRoadie's Avatar
Buried conduit, even conduit "buried" in a concrete slab, is a wet location.
MacRoadie is offline   Reply With Quote
Old 07-06-2009, 04:37 PM   #18
Electrical 101. Buried conduit = wet.
The Journeyman from Missouri needs to go back to school
I" is plenty big.
Four 90's max but shoot for 2 or 3.
Avoid close back to back 90's.
Use 45's or sweeping bends in the conduit whenever possible.
Pull the wire before you bury the conduit......just in case.
A bit of wire lube is really helpful.
220/221 is offline   Reply With Quote
Old 07-06-2009, 04:38 PM   #19
Exclamation
thanks everyone.
Old 07-06-2009, 06:55 PM   #20
Journeyman Wireman
Originally Posted by InPhase277 View Post
Article 100: Definitions. Location, Wet: Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
There are some of the sharpest electricians here, and some real good DIY'rs as well. This isn't like Mike Holt's forum where you would be ridiculed and beat down over it, but you got to stay on your toes, because you WILL be called out on it. I think it is fair to say that even the most experienced of us have learned something new at one time or another from this lowly DIY forum.
The wire inside the pipe is NOT in direct contact with the earth. UF would be overkill, more expensive and harder to work with.
jbberns is offline   Reply With Quote
Old 07-06-2009, 07:04 PM   #21
General Contractor
MacRoadie's Avatar
No, it's not, but the NEC doesn't care about the conduit. The code is referring to the conditions INSIDE the conduit, hence the reference to saturation (a point you actually made in your first post) and if you go to 310-8, it tells you what type of conductors can be used.
If the inside of a conduit is a dry location, then why would 310-8 even bother to list the type of conductors approved for wet locations? By your logic, any conductor can be used in a conduit buried below grade as the conduit should be considered a dry location.
Exactly when would you even use THHW if not in a conduit?
Old 07-06-2009, 07:13 PM   #22
Journeyman Wireman
My basement is underground. Do I need to rip out the romex and run uf inside of pvc?
Old 07-06-2009, 07:23 PM   #23
Electrical Contractor
kbsparky's Avatar
Most of the time, --- over time --- condensation can accumulate inside of buried conduits, even if they are watertight. They can fill up with water.
We run into this all the time, especially when removing conductors that have been in underground conduits for years. They come out soaking wet.
You are not permitted to install "dry locations only" wire into a wet location, which includes the insides of buried conduits.
-KB
Old 07-06-2009, 07:29 PM   #24
Rewards Points: 2,350
Your basement is not a enclosed area 1" in diameter. You can write the code making panels and submit a change recommendation, but until then, the NEC is clear that a conduit in the ground, or in concrete in contact with the ground, is considered a wet location. So inside your basement, the concrete is in direct contact with the earth, so any wiring inside the concrete itself, would need to be appropriate wiring for a wet location. Wiring in wooden stud walls is NOT in contact with the earth or with the concrete, so , unless you are using a spray washer in your basement, you can use everyday normal romex, NM-B.
I don't know about you, but I have pulled countless runs of wiring in pipe, in which each end of the pipe is inside a building, yet when the fish tape and head come out of the pipe, it is wet. You pull romex in underground pipes if ou want to, but I guarantee you that stuff is like a wick and will suck up water like a sponge. Conduits being wet locations is also one reason why the code requires them to be sealed if unused or after wire installation. Water will condense inside a panel through an underground feeder conduit. Usually have to pack them with duct seal. Or foam.
Old 07-06-2009, 07:32 PM   #25
Right, I wouldn't pull UF into the conduit. I would pull THHN/THWN.
Old 07-08-2009, 06:36 PM   #26
WFO
Bingo!
WFO is offline   Reply With Quote
Old 07-08-2009, 06:48 PM   #27
I use TWHN too
But from a DIY point of view - if the person is only making one run:
In order to do that they need black #12, white #12 & green #12
Many people won't go & find/buy individual wires
And then they need to know the exact length of wires or buy extra
OR buy a roll of each - which gets expensive
They believe the pre-made UF is "better"
Or they already have UF & don't want to buy more wire
I have way too much wire "in stock" at home
Wire, Conduit and Voltage Drop Questions kikdrum Electrical 9 03-01-2009 06:50 AM
Burial wire and a seeming difference of opinion... SxS Electrical 19 02-24-2009 09:16 AM
Conduit for #6 wire joey b Electrical 13 11-22-2008 12:13 PM
Installing Fluorescents in Garage rzrbkpk Electrical 26 04-08-2008 09:00 PM
pulling wire through old flexible conduit cbray Electrical 1 05-20-2005 03:55 PM