Old 04-29-2009, 05:02 PM   #1
Double Tapped Breaker
hello all,
at a recent home inspection, the inspector noted that a breaker was double tapped and this is not good because it could arc, one wire is for lights and the other is for the doorbell transformer, he mention i could use a 2 pole breaker like the one pictured here, is this true or safe?? what else could i do with the doorbell wire? put it on another seperate appropriate breaker?
http://www.drillspot.com/pimages/1565/156513_300.jpg
B2theRy is offline   Reply With Quote
Old 04-29-2009, 05:56 PM   #2
A "Handy Husband"
rjniles's Avatar
Remove the 2 wires from the breaker, wire nut them together with a single pigtail. Run the new pigtail to the breaker. You do not need to dedicate a breaker to a doorbell xformer.
Old 04-29-2009, 06:00 PM   #3
Electrical Contractor
Some breakers are made to be doubletapped, orwise just as the handy husband stated and you will be good to go.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 04-29-2009, 08:57 PM   #4
" Euro " electrician
frenchelectrican's Avatar
Most SqD and CH breakers are listed for doubletapped with two conductors at the termail screw however Double check the label to make sure { they are only allowed on 30 amp or smaller breaker size } I doubt that other are listed like that.
Otherwise just make a pigtail and wirenutted it and that will useally take care the issue there.
Merci,Marc
Double pole CH breaker ?? James Con Electrical 7 07-10-2008 12:41 AM
How Does A Double Pole Circuit Breaker Trip? shadowx360 Electrical 2 07-09-2008 03:44 PM
Three way light switches and double pole breaker ShawnColes Electrical 6 04-15-2008 09:25 PM
feed back voltage when using double breaker sluggermike Electrical 59 09-20-2007 03:37 PM