Old 06-02-2012, 05:59 PM   #1
Double tap or not?
Are these Square D breakers rated for two wires?
mk00 is offline   Reply With Quote
Old 06-02-2012, 06:30 PM   #2
Double tap or not?
Yes, Square D Homeline breakers are rated to accept two conductors. Just make sure if you're going to add something new, that you check the current load on the circuit to make sure you don't end up tripping the breaker with the new load.
LooseSCruz is offline   Reply With Quote
Old 06-02-2012, 06:42 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Double tap or not?
Yeah they are.
What happened, a home inspector call them out for the dreaded "double tap"?
Speedy Petey is online now   Reply With Quote
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
gregzoll (06-02-2012), LooseSCruz (06-03-2012)
Old 06-02-2012, 07:26 PM   #4
Licensed Electrician
k_buz's Avatar
Double tap or not?
IIRC, they are allowed to have two wires under the plate, but they have to be the same size wire.
Location...Location...Location
Old 06-03-2012, 01:35 AM   #5
" Euro " electrician
frenchelectrican's Avatar
Double tap or not?
The other thing it may come up is that you have quite few MWBC there so you will have to watch which circuits on each MWBC is hook up properly and If the MWBC not hook up properly you will burn the netural real easy.
There is a reason why is if you have two MWBC on the same phase or legs ( Line ) you will overload the netural real fast due it will be addtive.
If done properly ( over on two different phase or legs or line ) you will not get the netural overloaded at all.
But the only major quirk with MWBC is if any reason if you lifted the netural it don't have to be at the breaker box but it can be at the junction box as well once you lift the netural you can destory any 120 volt devices by inducing series connection ( some stuff will not affect but with electronique stuff sure no question asked )
Merci,
Marc
Tags
square d
Double switch wiring rockclimber Electrical 18 03-18-2012 11:13 PM
Changing A Double Switch to a single pole switch and a dimmer switch loydbrahn Electrical 0 11-09-2011 12:00 AM
Double Hung vs Single Hung CZSteve Remodeling 0 11-08-2010 08:29 AM
double pole breaker + outlets / x10 BlueBSH Electrical 0 09-09-2010 01:44 PM
Eliminating Double Taps in Older Sylvania 200A Panel Reilley Electrical 14 01-11-2009 05:52 PM