Does sub panel feed cable need staples withing 8"?
Feeding a 60A sub panel with 6/3 wire. Have fed it into panel but am wondering if, since it is clamped securely at the panel, if it needs to be stapled within 8" of the panel box like I need to do with my 12/2 wiring? It seems pretty thick to make those kinds of radii. Thanks in advance for your reply.
tpagel is offline   Reply With Quote
Old 05-29-2011, 06:18 PM   #2
Electrical Contractor
kbsparky's Avatar
No. The 8" rule is for boxes without clamps or cable connectors.
When using a regular cable connector, you are permitted a distance of 12" before you install the first strap. See NEC 334.30
-KB
Old 05-29-2011, 09:22 PM   #3
Missouri Bound's Avatar
The problem is that you need 4 wires to the sub panel. A ground must be run from the main. There are other things to consider with the ground as well, such as a seperate ground buss. And the neutral in the sub must be isolated from the ground and the panel.......there's always something.
Old 05-30-2011, 01:19 AM   #4
Scared Electrician
Saturday Cowboy's Avatar
Does not 6/3 actually contain 4 wires??? remember we don't count the ground
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
200 amp feed from 200 amp panel? JackDuich Electrical 17 03-29-2010 02:51 AM
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 08:40 PM
Sub panel gp_wa Electrical 21 08-20-2008 06:37 AM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 12:33 PM
Multiple Sub Panel Installation Handyman2007 Electrical 26 12-31-2007 06:47 PM