does the neutral have a voltage?
Lets supposed that we have a 3 phase Wye transformer 208/120V and one of the phases is out of valance with the neutral by lets say 20 Amps, something like phase 1 has a 100 amps load, phase 2 also 100 amps but phase 3 only 80 amps, in such case I been told the neutral will carry the 20 amps difference. Would I get zapped by the neutral under such or any other circumstances?
hvactech is offline   Reply With Quote
Old 03-11-2007, 08:38 PM   #2
Power Gen/RS Engineer
The neutral is typically "earthed" or connected to earth ground at the source. That being said, its ideal or theoretical voltage is 0 volts w.r.t. ground (i.e. your potential, typically). So, in theory, you should be able to touch it and not receive a shock. In the real world though, we know that given the finite resistance of the cabling, the voltage on the neutral will rise from 0 V at the earthing point (the transformer in your case) to some non-zero value at the load assuming that some current is flowing. As the current and length of cable increases so will the voltage rise measured to earth. What the measured voltage will be depends on a host of factors but why risk electrocution? Use the proper PPE and keep your (uninsulated hands off).
BigJimmy is offline   Reply With Quote
Old 03-11-2007, 09:03 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
EXACTLY!
It is unlikely the connected neutral will be carrying any noticeable voltage measured to ground, but it is most certainly carrying current in the state you describe.
I MUST say. Even though this is a "what if" question, 3-phase (ESPECIALLY 277/480) is NO place for anyone untrained to be messing around.
I truly hope this IS a "what if" question.
Old 03-12-2007, 06:05 PM   #4
scotch on the rocks
hvactech's Avatar
thanks a lot for the answers!!! I work with lots of 3 ph equipment and I’m always trying to learn more about the electrical side of it.
12v diff between ground and neutral at panel am9518 Electrical 7 02-25-2008 07:28 PM
Low voltage to vacuum l.schrankel@comcast.net Electrical 2 03-04-2007 10:38 AM
Why is this? Ron The Plumber Electrical 11 02-28-2007 06:14 PM
Suspected open/loose service neutral mrtomwj Electrical 5 09-28-2006 09:46 AM
Splice in Neutral to Panel - OK or Not? allpraisebob Electrical 4 08-12-2006 06:54 AM