While, technically, the joist with the JBox shown are not load bearing (it supported a formica 'false' ceiling) I don't think the NEC rules for JBoxes encompass this use.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
Old 04-30-2009, 09:12 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 478
Not the prettest box I've seen, but it seems to be installed in a way as to be flush with the ceiling.
As long as the box is mounted to something properly, I think it could be allowed.
Old 04-30-2009, 09:18 PM   #3
Learning by Doing
The Jbox is NOT screwed to the T&G (that's 9 inches above, I guess it's a little hard to tell from the pic). It's screwed to the plank on the left and right by way of the knock-outs and a few really big washers. The planks were toenailed to the adjacent joists and did not connect to each other - just the JBox.
I hate to see what would have happened if they hung a light fixture that weighed more than a pound or two.
Old 04-30-2009, 09:25 PM   #4
jbfan's Avatar
Rewards Points: 478
I can see it better now that you explained it to me.
Must be a light, light!
Old 04-30-2009, 09:32 PM   #5
Bigplanz's Avatar
Rewards Points: 990
314.23 (D) says:
(D) Suspended Ceilings. An enclosure mounted to structural or supporting elements of a suspended ceiling shall be not more than 1650 cm3 (100 in.3) in size and shall be securely fastened in place in accordance with either (D)(1) or (D)(2).
(1) Framing Members. An enclosure shall be fastened to the framing members by mechanical means such as bolts, screws, or rivets, or by the use of clips or other securing means identified for use with the type of ceiling framing member(s) and enclosure(s) employed. The framing members shall be adequately supported and securely fastened to each other and to the building structure.
(2) Support Wires. The installation shall comply with the provisions of 300.11(A). The enclosure shall be secured, using methods identified for the purpose, to ceiling support wire(s), including any additional support wire(s) installed for that purpose. Support wire(s) used for enclosure support shall be fastened at each end so as to be taut within the
ceiling cavity.
I guess it is somewhat subjective as to whether this is properly supported under the NEC, but I would subjectively say, no. It just doesn't look supported by either a framing member or approved support wire system.
Bigplanz is offline   Reply With Quote
Old 04-30-2009, 09:37 PM   #6
Bigplanz's Avatar
Rewards Points: 990
That's a big 'fail' on the adequate support provision. At least here in Louisville, this wouldn't pass.
Old 04-30-2009, 09:54 PM   #7
DIYer
I don't think a load bearing jbox would pass anywhere.
Gigs is offline   Reply With Quote
window rules? DangerMouse Building & Construction 8 04-17-2009 01:03 PM
Rules for furniture placement for a living room? Bacardi 151 Interior Decorating 17 12-23-2008 10:49 PM
What are the rules for a heavy up, between the pole and the meter. TW Lucas Electrical 2 05-10-2008 01:01 PM
Need nailing rules for attaching various mouldings ebola05 Carpentry 3 10-26-2007 07:45 PM
Design rules for wood floors in adjacent rooms chrish Flooring 1 09-10-2007 07:04 PM