Does NEC 300.14 Apply To Pig Tails? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-18-2010, 07:58 PM   #1
Does NEC 300.14 apply to pig tails?
The minimum length of conductors, including grounding conductors, at all boxes shall be 6". At least 3", of every conductor, shall extend outside the box.
Does this apply to pig tails when chaining receptacles? 54" (9x 6") seems like a lot of wire to get in the box.
deko is offline   Reply With Quote
Old 10-18-2010, 08:06 PM   #2
joed's Avatar
Rewards Points: 13,332
It applies to the wires the pigtails are attached to.
Old 10-18-2010, 08:11 PM   #3
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
it doesn't apply to the pigtails nor do the pigtails count in box fill.
speaking of; have you calculated box fill? It could be you are beyond the legal allowances.
Old 10-18-2010, 08:35 PM   #4
If pigtails do NOT have a required length, is there a best practice or accepted standard? I was thinking 4" seemed about right.
As for box fill calculations:
I have an outdoor receptacle (TR, WP) in a 20A chain (12/2 NM cable) that uses a metal box.
clamps on top and bottom of the box for the cable going in/out, and one grounding screw inside the box = 1
grounding conductors = 1
receptacle = 2
current carrying conductors = 4 (2 white, 2 black)
TOTAL = 8
8 x 2.25 = 18 cubic inches
Is this correct?
Old 10-18-2010, 08:58 PM   #5
nap
You talking to me?
nap's Avatar
fill calc looks correct. (a single duplex recep, right?)
pigtail length: whatever feels right 4" doesn't sound bad. I don't remember ever actually measuring them.
Old 10-18-2010, 09:06 PM   #6
yep, single duplex recep.
The box is 19 cu in so that's probably why it looked stuffed.
I'll go with 4" on the pigtails... just didn't want to give away the fact that I'm a newb too quickly when the inspector looks at it
Tags
chain , pig tails , receptacles
Benjamin Moore: "Do Not Apply to Bare Wood" Psoint Painting 4 03-18-2010 12:51 PM
Is there anything I could apply to drywall/plaster to determine if roof is leaking? kardplayer2k Roofing/Siding 5 02-07-2010 10:02 PM
Rotting rafter tails and fascia dave11 Roofing/Siding 1 10-20-2009 11:52 AM
Drywall Taping - do you apply a layer of mud over the tape on your first go? newbpainter Drywall & Plaster 20 05-18-2009 06:43 AM
What is the best way to apply stain to a deck? flashme18 Painting 4 04-24-2008 09:23 PM