Does Every Metal Box Need To Be Grounded? - Electrical - DIY Chatroom Home Improvement Forum
Old 09-11-2012, 06:03 PM   #1
Rewards Points: 1,062
does every metal box need to be grounded?
I was wondering if every metal receptacle need to be grounded via a green ground screw screwed in a hole in the back and connected to the other ground wires coming into and out of the box, in addition to the ground terminal of the possible power outlet or light for which the box is used. Also, if the box is used only as a JB, does it still need to be grounded?
Old 09-11-2012, 06:06 PM   #2
Rewards Points: 506
I don't believe it is a requirement that the screw be green.
jlmran is offline   Reply With Quote
Old 09-11-2012, 06:13 PM   #3
Yes and yes, it shall be a green screw
Bluehawks is offline   Reply With Quote
Old 09-11-2012, 06:14 PM   #4
Rewards Points: 506
Green screw citation?
The Following User Says Thank You to jlmran For This Useful Post:
gregzoll (09-11-2012)
Old 09-11-2012, 06:41 PM   #5
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
It doesn't have to be green...
Old 09-11-2012, 06:42 PM   #6
E2 Electrician
Every metal box needs to be bonded to the grounding conductor...
The Following User Says Thank You to stickboy1375 For This Useful Post:
amakarevic (09-11-2012)
Old 09-11-2012, 06:50 PM   #7
Rewards Points: 506
Yet, I believe it is possible for the box to BE the grounding conductor (e.g. Conduit?)
Old 09-11-2012, 06:54 PM   #8
E2 Electrician
The conduit would be the EGC.... and the box would be bonded by that wiring method.
Old 09-11-2012, 07:11 PM   #9
Rewards Points: 506
But couldn't the box act as (a part of) the EGC in the middle of a conduit run? Otherwise, what bonds one pipe to the other?
Old 09-11-2012, 07:22 PM   #10
Electrician
Rewards Points: 794
But how will the electrons know that it is a ground screw and not a regular screw.
darren is offline   Reply With Quote
The Following 2 Users Say Thank You to darren For This Useful Post:
amakarevic (09-11-2012), gregzoll (09-11-2012)
Old 09-11-2012, 07:24 PM   #11
bbo
well if there is one electron missing, you can be positive its a ground screw
bbo is offline   Reply With Quote
The Following 2 Users Say Thank You to bbo For This Useful Post:
gregzoll (09-11-2012), mpoulton (09-12-2012)
Old 09-11-2012, 07:31 PM   #12
Your title asks one question and your post asks another.
Does every metal box need to be grounded.....I would say yes. We could argue about special circumstances, but the rule is yes.
Your post asks if every metal receptacle needs to be grounded...I would say yes. A receptacle is not a box. Do you have to use the the green ground screw in the back of a metal box to ground a receptacle? Not necessarily. Some receptacles are self grounding. You could use a self grounding receptacle and attach it to a grounded box and would be fine.
Does a metal box containing wires that is just used as a junction box need to be grounded...Yes. I would use the equipment grounding conductor you pulled with the circuit and bond that to the back of the box via the pre-drilled and tapped hole that is provided.
Now, if you use metal conduit and properly connect your fittings to your metal boxes, then you would not have to use a green ground wire with your circuit. Your conduit would be your equipment ground and would take the place of the green ground wire. But you still would have to connect any grounding means from a light fixture, receptacle, etc to the back of the metal box via the pre-drilled and tapped hole that is provided.
Lets make this real simple. ALL METAL boxes, conduit, etc used in an electrical system needs to be grounded. How you ground them is where it gets interesting.
parman is offline   Reply With Quote
Old 09-11-2012, 07:31 PM   #13
It says in 250.126 that the terminal for the connection of the equipment grounding conductor shall be identified by one of the following:
1) A green, not readily removable terminal screw with a hexagonal head.
2) green, hexagonal, not readily removable terminal nut.
3) A green pressure wire connector. If the terminal for the grounding conductor is not visible, the conductor entrance hole shall be marked with the word Green or ground, the letters G or GR, a grounding symbol, or otherwise identified by a distinctive green color. If the terminal for the equipment grounding conductor is readily removable, the area adjacent to the terminal shall be similarly marked.
The Following User Says Thank You to Bluehawks For This Useful Post:
Julius793 (09-12-2012)
Old 09-11-2012, 07:41 PM   #14
Missouri Bound's Avatar
I'll add to the jocularity....if it's a ground screw it can't be positive
Do you want it your way or the right way?
Old 09-11-2012, 07:48 PM   #15
250.146 says that an equipment bonding jumper shall be used to connect the grounding terminal of a grounding type receptacle to a grounded box unless, it is a surface mounted box where you have direct metal to metal contact between the device yoke and the box.
Why can't you connect Ground/Neutral bus bars on a sub secutanudu Electrical 42 11-07-2012 01:33 PM
Combining old wire to new Cossack Electrical 148 08-26-2012 01:56 PM
I feel dumb - how to attach something to metal Zephie General DIY Discussions 3 07-11-2012 06:37 AM
Replacing metal box caused issues rivers001 Electrical 28 03-07-2011 12:21 AM
Grounded electrode on water pipe TW Lucas Electrical 7 05-12-2008 11:33 AM