I was wondering if every metal receptacle need to be grounded via a green ground screw screwed in a hole in the back and connected to the other ground wires coming into and out of the box, in addition to the ground terminal of the possible power outlet or light for which the box is used. Also, if the box is used only as a JB, does it still need to be grounded?
I think all of his questions have been answered, but not in one post. I'll attempt to do that.
By receptacle, the OP meant box. It was also established that the ground/bond screw does not have to be green. It also is implied in the answers that it is no good to just put in a screw if you do not connect it back to the grounding conductor coming into the box. The question is, "Does every metal box need to be grounded via a screw in the hole in the back of the box?" For safety, yes.
...in addition to the ground terminal of the possible power outlet or light for which the box is used.
If the "device yoke" is in contact with the metal box, then you probably do not need to run a ground wire to the device's ground screw. But if in doubt, running the extra conductor will not do any harm.
I would ground the junction box for the same reason as in question #1. If the bare hot wire comes in contact with the metal box, someone touching the box could receive a nasty shock. In the junction box, you'll wire nut the ground conductors anyway. Just add one more as a jumper/pigtail to the box's ground screw.
Your title asks one question and your post asks another.
Does every metal box need to be grounded.....I would say yes. We could argue about special circumstances, but the rule is yes.
Your post asks if every metal receptacle needs to be grounded...I would say yes. A receptacle is not a box. Do you have to use the the green ground screw in the back of a metal box to ground a receptacle? Not necessarily. Some receptacles are self grounding. You could use a self grounding receptacle and attach it to a grounded box and would be fine.
Does a metal box containing wires that is just used as a junction box need to be grounded...Yes. I would use the equipment grounding conductor you pulled with the circuit and bond that to the back of the box via the pre-drilled and tapped hole that is provided.
Now, if you use metal conduit and properly connect your fittings to your metal boxes, then you would not have to use a green ground wire with your circuit. Your conduit would be your equipment ground and would take the place of the green ground wire. But you still would have to connect any grounding means from a light fixture, receptacle, etc to the back of the metal box via the pre-drilled and tapped hole that is provided.
Lets make this real simple. ALL METAL boxes, conduit, etc used in an electrical system needs to be grounded. How you ground them is where it gets interesting.
250.146 says that an equipment bonding jumper shall be used to connect the grounding terminal of a grounding type receptacle to a grounded box unless, it is a surface mounted box where you have direct metal to metal contact between the device yoke and the box.
Here is the easiest way to show that your terminology is wrong, replace the word grounding with earth, and show me how that will clear a fault... Now, we bond everything to the ground(ed) (neutral) conductor to clear faults, not to the earth... the NEC needs to replace the wording of grounding with earth, and more people will understand the confusion.
Damn it.....all thats been accomplished here is that I just remembered that I forgot to bond my boxes to the ground in the last two outlets I put in......LOL
by "receptacle" i mean just a metal box.
by "outlet" i mean a power outlet, usually a duplex, AKA socket, into which you put the plug from a device or an appliance.
a "light" would be anything that provides illumination and is mounted to a receptacle.
so a receptacle most commonly hosts either an outlet, a light, or is a junction box
The box cannot be bonded by the 6-32 if the device is grounded.
A device may be grounded if the box is grounded under certain conditions.