04-20-2011, 05:29 PM
#31
Lost..
Do I need a sub panel here?
Originally Posted by mem
I don't think you are allowed to put romex inside a conduit anyway. Also, make sure the wire you use is THWN or dual rated THHN/THWN. Can't use straight THHN outdoors or underground as it is not waterproof.
And while I was at it, I'd just put in the 100 amp cable now for future expansion, unless you think you'll have a use for the 60 amp after the upgrade. You can still feed it with a 60 amp breaker at the main panel for now.
Thanks. I was recomended THHN by someone else. I didn't specifically mean "romex", I just meant sheathed cable that has several conductors inside a single sheath. Would it not be cheaper just to run individual wires? This would mean THWN single wires as opposed to an all inclusive THWN with all four wires present.
I understand the difference between THHN and THWN now that I read about them. THHN is for heat only, THWN is for underground applications.
04-20-2011, 05:40 PM
#32
Lost..
Ok. just got off the phone with a local electrical supply house.
He said they don't even make THWN anymore. (?)
He said in order for it to be burried (conduit or not - it doesn't matter) it would have to be UF rated, and he had 6-3 UF at $2.60/ft
He said if I went to alluminum wire, it would be 2 size URD and it was around $1.54/ft.
Also priced #6 cable in individual strands and it was about $1/ft that way. That would mean to do it in individual strands it would cost about $4/ft as opposed to the all inclusive cable which is $2.60/ft. So, the all inclusive cable is cheaper than individual wires.
04-20-2011, 06:23 PM
#33
A "Handy Husband"
Most wire is dual rated THHN / THWN these days
Below is a copper amperacity chart. You can use copper THWN #6 AWG for the 3 current carring conductors and #10 for the ground. You will need 2 ground rods at the garage.
Normal House Wiring Gauge
Consult your building inspector
because your location
will have a specific building code! Circuit
Maximum
Amperage Minimum COPPER
wire gage
15A 14AWG
20A 12AWG
30A 10AWG
45A 8AWG
60A 6AWG
80A 4AWG
100A 2AWG
I think he was sizing the AL wire at 100 amps, not 60 as you are planning.
IMO, going larger than 60 amps is overkill and a waste of money
Coastal South Carolina
04-20-2011, 09:23 PM
#34
Lost..
Maximum
wire gage
15A 14AWG
20A 12AWG
30A 10AWG
45A 8AWG
60A 6AWG
80A 4AWG
100A 2AWG
So it sounds like I would need three strands of 6AWG and one strand of 10AWG. This is assuming I can actually run THHN/THWN type wire. Priced at Lowes, the 6AWG is about $.60/ft.
I'm still not sure whether or not I can run THHN/THWN or if it has to be UF. I looked through the NEC today trying to find a place where says, but I had no luck. If anybody is willing to check that out for me I would appreciate it. I am aware there are local codes as well, but I am oconcerned with the NEC at the moment.
In alluminum wire, Lowes had 2,2,2, but it was only 2 conductors and ground. If I used Aluminum wire, what size or description would I need?
04-20-2011, 11:16 PM
#35
A "Handy Husband"
If you use aluminum THWN, you need #4 for the 3 current carrying conductors and 1 #8 for the ground.
You could use copper UF for the feeder as direct burial at 24 inch depth. The size would be 4-3 (#4 AWG, 3 conductor plus bare ground. As you see copper THWN has a greater amperacity than copper UF. THWN #6 vs UF #4 for the 60 amp feeder.
04-21-2011, 09:20 AM
#36
Licensed Pro
While RJ has a good point about only needing 60A at the sub, I would look into using the Al 2-2-2-4 mobile home feeder for your run as it will be the most cost effective and allow for upping the feed to 90A if needed. It is rated as USE-2 so it can be direct buried or placed in conduit. Most lowes don't carry it, but HD does as well as most electrical suppliers.
As to your question about THHN/THWN, yes it can be placed in buried conduit. If you use 6/3 UF in conduit, you will find it to be difficult to pull because of its size (wide and flat).
04-21-2011, 09:35 AM
#37
A "Handy Husband"
Before you direct bury mobile home feeder, read these posts:
http://www.garagejournal.com/forum/s...ad.php?t=44176
If you go with this product, use conduit to protect it.
04-21-2011, 10:28 AM
#38
Licensed Pro
I would agree, it's always better to use conduit when possible.
04-21-2011, 10:49 AM
#39
Lost..
Just called the same electrical supply house and asked if they carried 2,2,2,4 mobile home feeder. Yes, and it is $1.50/ft. This will probably be the most cost effective, and it will allow me to run a bigger breaker at the main panel - say 90amp. This would allow for future expansion.
Now I'm trying to figure out if it is within code to use it. I am not going to call my building inspector and ask. I don't want them to have any idea that I am even thinking about looking into this.
I wish there was some way that I could call them and see if I could use it, just to get the answer. If I call though, they know I am in the city limits and they are just going to tell me to not worry about it. They will tell me a licensed electrician has to do it anyway, so it doesn't concern me.
04-21-2011, 10:57 AM
#40
Licensed Pro
If you are trying to sneak this in and do the work without a permit DON"T!! It is in your best interest to have the inspector approve what you are doing and how it is done.
04-21-2011, 11:10 AM
#41
A "Handy Husband"
JSM
It is not the purpose of this forum to provide advice or encourage the willful violation of ordinances or permit requirements. I encourage you to call and discuss with an electrical inspector.
Doing un-permitted work can have many bad consequences
1 Unsafe electrical work
2 Insurance difficulties if you have a claim
3 Future home sale may be difficult if inspector finds un-permitted work.
Many localities (especially in Alabama) allow home owners to do this work.
The Following User Says Thank You to rjniles For This Useful Post:
#42
Lost..
Oh trust me I plan on getting it done right, I am just trying to find out what needs to be done so I don't sound like an idiot when I actually do get a contractor to show up. It should be noted that I have put in calls to at least 10 electrical contractors over the past three weeks, and not yet have I gotten somebody to even come by and look at it.
I want to know what my options are in case they try to tell me something different.
The Following User Says Thank You to J S Machine For This Useful Post:
04-21-2011, 03:09 PM
#43
Lost..
I drew up this illustration. If you guys don't mind, let me know if this is correct. I think I have everything correct.
EDIT Updated pic to show grounds I forgot to draw for the 12-2 NM wire.
04-21-2011, 04:02 PM
#44
Nice drawing JS. Presumably, the lights and outlets will be on grounded circuits as well? As I understand it, the neutral buss bar must NOT be bonded to the subpanel and you'll need additional grounding rods at the sub connected with a minimum of #6 copper. I sure someone with come by with the actual code application as I've already told you more than I know!
04-21-2011, 04:05 PM
#45
Lost..
Yes you are correct. Knew I'd forget to add something. That is regular 12-2 romex type wire with 2 conductors (hot/neutral) and ground. I just forgot to draw the ground..lol
Just fixed that. New pic added with correct ground routing.
| Thread Tools |
Search this Thread |
| Display Modes |
Linear Mode