Old 11-11-2010, 06:32 AM   #1
Do I need a ground rod to replace copper water pipe
2 threads on same issue merged
I am replacing my water main with PEX plastic pipe. My house is plumbed with copper pipes. The old polybutylene pipe I am replacing was connected to about 5 feet of copper that extended under the ground right outside of the foundation. This was one source of a leak that prompted this water pipe replacement. I am assuming this copper pipe is part of the grounding system for the house as the electric panel box on the other side of the house is connected to the cold water pipe with copper wire and a clamp. There is also one ground rod outside of the panel box on that other side of the house. I want to run the PEX straight from the water main and through the foundation and eliminate that underground water connection.
My question is: should I put a ground rod where the water main comes through the foundation and connect it with copper wire to the copper pipes in the crawspace to replace the loss of the copper tubing that was under the ground?
Thanks for your input.
Mike
mfkcbk is offline   Reply With Quote
Old 11-11-2010, 06:41 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Why not just cut it off inside and leave the pipe as an electrode?
Old 11-11-2010, 07:07 AM   #3
The service panel requires a ground rod driven into the ground.
Old 11-11-2010, 07:52 AM   #4
Right, and there is already one on the outside of the house connected to the panel box.
Should I put a second grounding rod where the water main comes throught the foundation since thats where the copper water pipe originally came through? The water main and electric panel are on opposite sides of the house.
Someone told me not to, but rather I should put a 2nd ground rod 6 feet from the first one and connect the two and not put one where the water main comes in. I just don't know which is correct.
Thank you.
Mike
Old 11-11-2010, 09:14 AM   #5
Xtreme DIY'r
2nd rod where the 1st rod is located is correct
I'd also make sure the copper pipe in the house is still connected/bonded to the panel
Old 11-11-2010, 12:47 PM   #6
If you leave the pipe in the ground, solder a cap on the end inside.
OT: If a fuel oil tank is decommissioned, the filler pipes need to be removed, or if that is not possible, capped at both ends.
This is to prevent accidental re-use.
The disadvantages of crab apple trees. In summer, the apples are too sour to pick and eat. In winter the birds come and leave dropping all over the place.
Old 11-11-2010, 04:18 PM   #7
If you don't have a water main grounding source, 2nd ground rod is required. It has to be put atleast 8' apart from each other iirc
heartlessmcfly is offline   Reply With Quote
Old 11-11-2010, 04:37 PM   #8
Thanks for all the reply's. I will put a 2nd ground rod in 8 feet from the first one. That's easy enough.
I'd already cut out the copper water pipe that went through the foundation in order to put a temporary water main in using the PEX while I'm doing my trenching. At this point it would be more trouble to reconnect the copper, cap it and leave it buried.
The more I read and hear about grounds, the more confused I get. For example, I don't understand why 2 rods are needed and why they need to be connected together but spaced apart. Also why would I not just put a ground rod on the other side of the house where the original water main came, run the wire throught the foundation, and connect to the copper plumbing there? It seems like that would be the equivalent of what I originally had.
Mike
Old 11-11-2010, 04:41 PM   #9
The ground rods do not connect to each other. A seperate wire from each to the panel.
Old 11-11-2010, 05:02 PM   #10
Not true. A second rod is a supplemental rod and is NOT required to be run form the panel. All that is needed is a jumper from one to the other.
Also, it is six feet apart minimum, not 8'.
Old 11-11-2010, 05:03 PM   #11
Do it right.
Mike
You only need one ground rod if you can verify that its resistance is 25 ohms or less, if you install 2 rods the nec basically says you tried hard enough. also they must be spaced 6 feet apart not 8. 8 feet of rod needs to be below ground level so if your using an 8' rod, the entire piece must be below the soil.
also the 2 rods ARE to be connected together, and then tied into the nuetral bus bar.
SubSailor is offline   Reply With Quote
wht is te mximum prussure of the water streem in asolderd joints copper pipe bawab55@hotmail Plumbing 2 06-28-2010 09:58 AM
PEX pipe and sharkbite slowing water flow? Snav Plumbing 1 04-09-2010 04:32 PM
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 08:40 PM
Preference for installing tub spout? dolvio Plumbing 7 02-11-2009 11:53 PM
Is 1/2 Pex more restrictive than 1/2 copper? twilightcall Plumbing 19 06-24-2008 08:32 AM
