DIY 200A Main Service Upgrade? - Electrical - Page 4 - DIY Chatroom Home Improvement Forum
Old 09-04-2008, 05:36 PM   #46
Licensed Electrician
jrclen's Avatar
Rewards Points: 514
Originally Posted by Philip_Soldat View Post
Gotcha, so perhaps I may not even need the 200A... but in any case I am solid with the procedure from here on, TONS OF THANKS!!!!!
Without doing an actual load calculation it's hard to tell. But a 150 amp service will power a lot of stuff. Let us know what you do and how it turns out. Any more questions, just come back and ask.
John
jrclen is offline   Reply With Quote
Old 09-04-2008, 07:44 PM   #47
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Originally Posted by jrclen View Post
Exactly, that is the sum of the breakers. Your 30 amp dryer will typically run at 22 amps. Your 50 amp range will use less than 20 when cooking the typical meal. Your 20 amp projector might use 6 amps when running. And not everything is running at once. This is why we can install 40 circuit panels with only 200 amp mains.
In my house I have a 100amp main panel, a 70amp sub panel, and a 60amp subpanel in the garage. The total of the breakers is 560 amps. I have never seen more than 70 amps total load on the mains with the AC and dryer running.
JR: What kind of device / meter are you using that allows you to see the amps you are currently drawing?
Jamie
jamiedolan is offline   Reply With Quote
Old 09-04-2008, 07:53 PM   #48
Jamie
http://www.theenergydetective.com/st...s/ted1000.html
jerryh3 is offline   Reply With Quote
Old 09-04-2008, 09:18 PM   #49
Ok then I will run the subpanel and hook up the spa, get my inspections, then calculate my total load just to be sure (real time). I am handling a lot more projects as well, so I will try to take pics and provide details, hope its as helpful to others as it;s been for me.
Philip_Soldat is offline   Reply With Quote
Old 09-04-2008, 09:21 PM   #50
Rewards Points: 506
Send a message via AIM to theatretch85
Jerry that is amazing, Now I might actually have to buy one with the PC hookup! I have a cheap clamp meter I bought a while ago on ebay and and as cheap as it is its worked perfectly every time. I have a tendency to do some rather large holiday lights displays in the winter here and the clamp meter is a MUST to balance out all the various loads. I have a distribution box that I built a while ago that has a 4 pole relay inside, with several 20 amp outlets on the outside. Balancing out the loads not just so that each outlet/contact only has up to 20-22 amps, but that I have it balanced out in the main panel as well. I tripped the 100 amp main a few times because I didn't quite have it balanced out and had one leg overloaded. I was nearly maxing out the 100 amp service into the house, when the weather warmed up, the lights would turn on and trip the breaker.
That TED device would be nice to monitor the power being consumed at any given time of the day and to better determine where all the power is going (electric bill is usually over 200 a month, with all gas appliances).
theatretch85 is offline   Reply With Quote
Old 09-05-2008, 09:04 AM   #51
jrclen's Avatar
Rewards Points: 514
Jamie
It's called an amp clamp. Here is a link to some quality meters. The cheaper one shown will work great for home and DIY use.
http://www.specialized.net/ecommerce...e+Clamp+Meters
What it will not do is tell you how much power you use over time. Like a watt hour meter. But it will give you a reading for how much current is flowing through a wire at any given time.
John
Old 09-05-2008, 09:58 AM   #52
DIY'er
jamiedolan's Avatar
Thanks for the link. Will any Meter that has a AC AMP setting do the same thing?
Basically does a meter like this just tell you the current draw on any like that it is clipped onto?
Jamie
Old 09-05-2008, 10:51 AM   #53
jrclen's Avatar
Rewards Points: 514
Jamie
Some meters measure milli amps with probes. They will fry if put in series with a typical load in a electrical circuit in your house.
The clamp around the wire reads how many amps are currently flowing though the wire. It needs to be clamped around only one wire. If you clamp it around a cord for instance it will read 0 as the hot and return are canceling each other out.
John
Old 09-06-2008, 12:34 PM   #54
DIY'er
jamiedolan's Avatar
Thank you for the information about the clamp meters. I was able to obtain one and it is proving to be very useful. I will make a new post about it, as I am really kind of off topic for this conversation.
Jamie
Old 09-07-2008, 11:02 AM   #55
DIY Junkie!!
Rewards Points: 182
Be sure to come back and let us know how it turns out, Philip!
Dugly
YerDugliness is offline   Reply With Quote
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
2x100a sub on service main jambud Electrical 17 03-12-2008 09:31 AM
Main disconnect box before service panel Cellomangler Electrical 4 02-04-2008 07:43 AM
Service upgrade rondo Electrical 1 05-21-2007 06:19 PM
Arced main lug in service panel burgeke Electrical 4 11-02-2006 11:28 AM