Divide Neutral On Subpanel? - Electrical - DIY Chatroom Home Improvement Forum
Old 11-17-2011, 03:22 PM   #1
I've got a 100amp subpanel from a 200amp service planning on using #3 copper THHN.
The nuetral bar on the main service is only large enough to handle #6.
Can I run two #3 hots and two #6 nuetrals instead of two #3 hots and 1 #3 nuetral?
chisouth is offline   Reply With Quote
Old 11-17-2011, 03:25 PM   #2
Sparky
Rewards Points: 510
no.
you need to buy an "add-a-lug" for your main panel. if you tell me which brand i can try to pull a cat # for you
Techy is offline   Reply With Quote
Old 11-17-2011, 03:25 PM   #3
Can you install one of these on the neutral bar?
brgmgb is offline   Reply With Quote
Old 11-17-2011, 03:32 PM   #4
Licensed electrician
Rewards Points: 1,502
There are lug kits that will fit in the screw holes in the buss. For a Square D panel you would use a LK70AN. You can google the image to see what they look like.
Old 11-17-2011, 04:06 PM   #5
Nice!
Had no idea they made these, I'll have to try and see what my type my panel will take the LK70AN looks like it would work if those two prongs each go into one screw hole.
I'll upload a picture of my main panel if I'm having some issues.
Thanks Everybody.
Old 11-17-2011, 04:52 PM   #6
JOATMON
ddawg16's Avatar
Rewards Points: 1,458
You may already understand why.....but just in case....
While it seems logical that 2 #6's are equal to 1 #3.....they are not...but more importantly....if one of the #6's were to come loose, now all of the return current would be in the other #6 wire......result may not be pretty.
ddawg16 is online now   Reply With Quote
Old 11-18-2011, 07:37 AM   #7
I agree with the answer that you should NOT use two #6s in place of a #3. But I did the math and the total area is amazingly close. A #3 AWG has a diameter of 0.2294 inches giving it a cross-section area of 0.041331 sq inches. A #6 has a diameter of 0.1620 inches. Two #6s have a total area of 0.041224 sq inches. It doesn't work out that close for any other wire size. For example, two #12s (with total area of 0.010255 sq inches) do not equal a single #6 (with area of 0.020612 sq inches).
Old 11-18-2011, 08:29 AM   #8
Banned Electrician
HARRY304E's Avatar
Rewards Points: 204
That panel should already have a neutral lug that is the same size as the lugs for hots.
310.10(H)
(H) Conductors in Parallel.
(1) General. Aluminum, copper-clad aluminum, or copper
conductors, for each phase, polarity, neutral, or grounded circuit
shall be permitted to be connected in parallel (electrically
joined at both ends) only in sizes 1/0 AWG and larger where
installed in accordance with 310.10(H)(2) through (H)(6).
HARRY304E is offline   Reply With Quote
Old 11-18-2011, 11:00 AM   #9
JOATMON
ddawg16's Avatar
But still are not equal......the 2 #6's are 0.3% smaller....
(shssssss....don't want to encourage the OP)
Yea....I know....so close they might as well be equal.....just don't want to give anyone any ideas.....
Old 11-18-2011, 11:12 AM   #10
Picked up the add-a-lug last night and installed the panel.
I hear what you guys are saying about the parallel neutral, someone suggested it to me and it didn't sound kosher to me either.
Thanks again for the advice.
Old 11-18-2011, 12:21 PM   #11
Rewards Points: 130
Use one of these. Sorry I was so late with the picture.
Tags
nuetral , sub panel , subpanel
Bonded Ground & Neutral in 240v subpanel RST Electrical 22 11-04-2011 01:18 PM
Bond subpanel Neutral directly to SE neutral using split bolt? Sierevello Electrical 1 01-30-2011 08:08 PM
Sharing Neutrals on the same phase electro Electrical 30 08-12-2010 02:10 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 04:58 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 11:33 AM