Discussion on switch grounding/bonding


Is this discussion more about bonding rather than grounding? Or not?

jlmran is offline   Reply With Quote
The Following User Says Thank You to jlmran For This Useful Post:
jakeandamy (04-25-2011)
Old 03-16-2010, 08:48 PM   #2
Member
 
Join Date: Feb 2010
Location: Oklahoma
Posts: 978
Default

Discussion on switch grounding/bonding


If we're going to be weekend experts (a.k.a. - DIYers) then we should at least use the correct terminology.

The body of the switches (and other devices) are not grounded, they are bonded (using a bare or green wire) ultimately to the neutral bus bar at the main service panel.

The act of grounding is simply driving a rod into the earth and attaching it to the neutral bus bar, through a (usually) bare conductor. Grounding also occurs when utility companies bond the case of a transformer (using a conductor) to the bottom of the pole, underground.

jlmran is offline   Reply With Quote
Old 03-16-2010, 09:14 PM   #3
Member
 
Join Date: Sep 2008
Location: Oregon
Posts: 1,497
Default

Discussion on switch grounding/bonding


The terms "grounding", "grounding screw", etc. are used in product documentation like this...
http://assets.twacomm.com/assets/pdf/19139.pdf

http://www.leviton.com/OA_HTML/ibeCC...minisite=10026
Billy_Bob is offline   Reply With Quote
Old 03-16-2010, 09:16 PM   #4
nap
You talking to me?
 
nap's Avatar
 
Join Date: Dec 2007
Location: sw mi
Posts: 5,407
Default

Discussion on switch grounding/bonding


Quote:
Originally Posted by jlmran View Post
If we're going to be weekend experts (a.k.a. - DIYers) then we should at least use the correct terminology.

The body of the switches (and other devices) are not grounded, they are bonded (using a bare or green wire) ultimately to the neutral bus bar at the main service panel.

The act of grounding is simply driving a rod into the earth and attaching it to the neutral bus bar, through a (usually) bare conductor. Grounding also occurs when utility companies bond the case of a transformer (using a conductor) to the bottom of the pole, underground.




by stating it is connected to the neutral, while technically correct (but only at the service disconnect),it is going to confuse the daylights out of a lot of folks and possibly cause them to connect the yoke of the switch to the wrong conductor.

the yoke of the switch is connected to the equipment grounding conductor.

and I haven't used a bare GEC in my entire tenure as an electrician.

and since a device that is listed as self grounding, not self bonding, I suggest we stick with the terms that are commonly used where they are used.

Last edited by nap; 03-16-2010 at 09:20 PM.
nap is offline   Reply With Quote
Old 03-16-2010, 09:18 PM   #5
Member
 
Join Date: Feb 2010
Location: Oklahoma
Posts: 978
Default

Discussion on switch grounding/bonding


Yeah, also in cables, like "12-2 with ground", etc. But we're better than that because we have a deeper understanding of what is really happening.
jlmran is offline   Reply With Quote
Old 03-16-2010, 09:21 PM   #6
Member
 
Join Date: Feb 2010
Location: Oklahoma
Posts: 978
Default

Discussion on switch grounding/bonding


Quote:
Originally Posted by nap View Post
the yoke of the switch is connected to the equipment grounding conductor.
Or, more accurately, the yoke of the switch is connected to the equipment bonding conductor.

If this confuses folks then a good shock might allow them to become unconfused.
jlmran is offline   Reply With Quote
Old 03-16-2010, 09:23 PM   #7
Member
 
Join Date: May 2009
Location: Brooklyn, New York (NYC)
Posts: 1,124
Exclamation

Discussion on switch grounding/bonding


Quote:
Originally Posted by nap View Post
because all metal parts that might become energized must be grounded. If the yoke of the switch becomes energized, if using a plastic box, it would not trip the breaker.

since the plate screws contact that metal yoke, the screws would then be energized.

so, if you touched the screw and anything that is grounded, you get zapped.
the same (non-desirable) effect would be in an un-grounded metal box! (IMHO)!
spark plug is offline   Reply With Quote
Old 03-16-2010, 09:26 PM   #8
Member
 
Join Date: May 2009
Location: Brooklyn, New York (NYC)
Posts: 1,124
Lightbulb

Discussion on switch grounding/bonding


Quote:
Originally Posted by jlmran View Post
Or, more accurately, the yoke of the switch is connected to the equipment bonding conductor.

If this confuses folks then a good shock might allow them to become unconfused.
It's all Semantics! But, as you suggest. "A good, shock might Allow? them to be UN-confused!!
spark plug is offline   Reply With Quote
Old 03-16-2010, 09:31 PM   #9
Member
 
Join Date: May 2009
Location: Brooklyn, New York (NYC)
Posts: 1,124
Thumbs up

Discussion on switch grounding/bonding


Quote:
Originally Posted by BlueBSH View Post
You should explain that to the people that built my house *lol* I went around checking all the switches and outlets for ground... they did a good job on the outlets, but not one switch was grounded... been going around doing that myself.... ugh
are the boxes (UN)-Grounded? (But the switches not bonded to the grounding connector!) Then, you might not be up to the latest Code. But you DO have ground protection. And you're fine. Because it's EXISTING!!
spark plug is offline   Reply With Quote
Old 03-16-2010, 09:31 PM   #10
Member
 
Join Date: Feb 2010
Location: Oklahoma
Posts: 978
Default

Discussion on switch grounding/bonding


Quote:
Originally Posted by spark plug View Post
It's all Semantics! But, as you suggest. "A good, shock might Allow? them to be UN-confused!!
I wouldn't wish injury (or worse) on ANYBODY. But, one should be smart enough to know when enters a realm beyond their capacity. One way to extend one's capacity is to gain education...using correct terminology and concepts.
jlmran is offline   Reply With Quote
Old 03-16-2010, 09:43 PM   #11
Member
 
Join Date: May 2009
Location: Brooklyn, New York (NYC)
Posts: 1,124
Thumbs up

Discussion on switch grounding/bonding


Quote:
Originally Posted by Scuba_Dave View Post
I've been upgrading my switches in my house
Wires have a ground, but its grounded to the metal box - wrapped around the wire & under the clamp
As I go around I have added a wire from the grounding screw to the box
I do have quite a few metal face plates in my house
On metal boxes, if the box is Grounded and the switch not (Bonded to the box) you're fine. Because the Band (of the switch) is making contact with the box while it's attached. The main reason (IMHO) why the Code was revised to require the Switch to be bonded to the Grounding conductor, is because of the widespread use of Plastic boxes.!
spark plug is offline   Reply With Quote
Old 03-16-2010, 09:52 PM   #12
Member
 
Join Date: May 2009
Location: Brooklyn, New York (NYC)
Posts: 1,124
Thumbs up

Discussion on switch grounding/bonding


Quote:
Originally Posted by jlmran View Post
If we're going to be weekend experts (a.k.a. - DIYers) then we should at least use the correct terminology.

The body of the switches (and other devices) are not grounded, they are bonded (using a bare or green wire) ultimately to the neutral bus bar at the main service panel.

The act of grounding is simply driving a rod into the earth and attaching it to the neutral bus bar, through a (usually) bare conductor. Grounding also occurs when utility companies bond the case of a transformer (using a conductor) to the bottom of the pole, underground.
I beg to differ. As was discussed in other posts on this thread. A switch, when attached to a Grounded metal box (as in the case of Scuba Dave) is considered Grounded (and in fact, is.) But since the proliferation of plastic boxes, the Code has been revised to require the switch to be also "Bonded" to the Grounding conductor in the box! !
spark plug is offline   Reply With Quote
Old 03-16-2010, 09:55 PM   #13
Member
 
Join Date: Feb 2010
Location: Oklahoma
Posts: 978
Default

Discussion on switch grounding/bonding


Quote:
Originally Posted by spark plug View Post
I beg to differ. As was discussed in other posts on this thread. A switch, when attached to a Grounded metal box (as in the case of Scuba Dave) is considered Grounded (and in fact, is.) But since the proliferation of plastic boxes, the Code has been revised to require the switch to be also "Bonded" to the Grounding conductor in the box! !
This assumes that the NEC is written using correct terminology. I agree...it is semantical.
jlmran is offline   Reply With Quote
Old 03-16-2010, 10:00 PM   #14
Member
 
Join Date: May 2009
Location: Brooklyn, New York (NYC)
Posts: 1,124
Thumbs up

Discussion on switch grounding/bonding


Quote:
Originally Posted by jlmran View Post
I wouldn't wish injury (or worse) on ANYBODY. But, one should be smart enough to know when enters a realm beyond their capacity. One way to extend one's capacity is to gain education...using correct terminology and concepts.
I agree with you 100%. But, assuming the work is left to experts. The rest IS semantics. (One of my hobbies, as you can see in my profile.)!
spark plug is offline   Reply With Quote
Old 03-16-2010, 10:01 PM   #15
nap
You talking to me?
 
nap's Avatar
 
Join Date: Dec 2007
Location: sw mi
Posts: 5,407
Default

Discussion on switch grounding/bonding


Quote:
Originally Posted by jlmran View Post
Or, more accurately, the yoke of the switch is connected to the equipment bonding conductor.

If this confuses folks then a good shock might allow them to become unconfused.

NO NO NO

it is attached to the equipment grounding conductor. the EGC is the term the NEC uses and we should not attempt to alter that.

nap is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Light switch installation problems pc_clone Electrical 8 11-30-2009 09:25 PM
Modification to an existing pump switch DRBLKJK Electrical 10 08-23-2009 03:06 PM
4 way switch confusion Richo Electrical 10 04-09-2009 07:11 AM
Replacing a bathroom fan switch cmacjr22 Electrical 4 11-04-2008 06:14 PM
Basic Switch wiring question; Dimmer to Toggle switch (Pictures included) inspectator Electrical 8 08-07-2007 01:19 AM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.