Disconnect For Mini Split - Electrical - DIY Chatroom Home Improvement Forum
Old 06-17-2013, 11:02 AM   #1
Disconnect for Mini split
I need to install a disconnect for a mini split heat pump. these are the power specs.
Outdoor Unit Power 208-230/VAC-1Ph-60Hz
Available voltage range 187-253VAC
Fuse Size, Max 30A
MCA 15.5A
what size wire would I use and is there a special way to hook it up. would the inside breaker be 15A and fuses no bigger than 30A. Any info would appreciated.
Anthony M
amoscara is offline   Reply With Quote
Old 06-17-2013, 11:19 AM   #2
Inside breaker would be 30a. I would use #12 wire
davenc is offline   Reply With Quote
The Following 2 Users Say Thank You to davenc For This Useful Post:
amoscara (06-17-2013), darren (06-17-2013)
Old 06-17-2013, 11:21 AM   #3
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
You need to wire it with #12 and your breaker can be up to 30 amps. I wouldn't go less than 25. You'll feed the condenser and the AHU is wired off of that.
On a mini-split, the disconnect would just go outside with the condenser.
wirenut1110 is offline   Reply With Quote
The Following User Says Thank You to wirenut1110 For This Useful Post:
Old 06-17-2013, 11:27 AM   #4
Thanks for the quick reply guys.....what size fuses for disconnect and should I use 12/2 or 12/3.
Anthony M
Old 06-17-2013, 11:35 AM   #5
Rewards Points: 510
12/2 to the disconnect, provided the wiring isn't outside. Then from the disconnect to the condenser with some liquid tight conduit and THHN wire.
The disconnect outside should just be a non-fusible pull out. The breaker is the "fuse".
Old 06-17-2013, 11:56 AM   #6
The disconnect will be mounted on the house and the wire will enter through the rear of the box.
Old 06-17-2013, 12:05 PM   #7
Rewards Points: 510
That's cool.
There needs to be a receptacle within 25 feet and on the same level for servicing.
Old 06-17-2013, 01:20 PM   #8
I do have a 15A outdoor receptacle which will be about 4' away from the disconnect, would that good. Also what does MCA 15.5A mean
Old 06-17-2013, 01:44 PM   #9
Rewards Points: 510
Yes, the receptacle is fine. MCA= minimum circuit ampacity. So, you have to have a circuit that can handle a minimum of 15.5 amps and the maximum breaker size is a 30. Different rules apply to motors and HVAC equipment.
Old 06-17-2013, 03:50 PM   #10
One more question...should the 30A breaker be a single or double pole...Im thinking double if I need 230......
Old 06-17-2013, 03:51 PM   #11
JW
mm11's Avatar
Rewards Points: 606
Double pole
mm11 is offline   Reply With Quote
The Following User Says Thank You to mm11 For This Useful Post:
Old 06-17-2013, 05:11 PM   #12
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
You could run #14 AWG if you wanted.
Also, nobody ever does this, but a disconnect is required on the inside as well... just saying.
Old 06-17-2013, 08:22 PM   #13
Rewards Points: 510
I was wondering about that 'cause I had heard some talk about it and never researched it. Is that an '08 or '11 thing?
Old 06-17-2013, 11:02 PM   #14
" Euro " electrician
frenchelectrican's Avatar
Fuse Size, Max 30A
MCA 15.5A
Anthony M
Just becarefull with this part some inspectors will nail ya on this part.
Did the nameplate mention breaker as well ? if so you are good to go.
Normally for moi .,
Using the NEC art 430 et 440's
The conductor size is 14 awg size but normaly 12 awg will work just fine for this purpose
Max OCPD ( it can be breaker or fuse if the nameplate say either one or both ) will be 30 amp.
But a gotcha is if your unit say fuse only then install the outdoor fuseable A/C disconnect switch and install 30 amp time delay fuse that will take care of that ( the breaker can be still at 30 amp in the breaker panel )
I belive that was changed not too long ago but not sure which cycle they did enforce this part.
Merci,
Marc
Old 06-18-2013, 02:48 AM   #15
Rewards Points: 1,192
Coming up through the ranks,I was always taught if you are feeding a fusible disconnect,you used wire size to compliment size of disconnect and fuse down at that point.
bobelectric is offline   Reply With Quote
Question: Backfeeding Gen thru Pull-Out Disconnect and GFCI (with interlock kit) diyfram Electrical 7 11-02-2012 10:59 AM
Split Buss? how to disconnect power? tom1973 Electrical 4 01-05-2012 01:01 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
30A Air Conditioner Disconnect JPWMU Electrical 6 04-19-2010 03:55 PM
Main disconnect neutral wiring Daniel Holzman Electrical 5 10-04-2009 01:36 PM