-   -   Diagram for 3 way ceiling fan light switch (http://www.diychatroom.com/f18/diagram-3-way-ceiling-fan-light-switch-163942/)
Aurora65 11-19-2012 05:37 AM
Ceiling fan light 3 way wiring problem
I'm trying to wire two 3-way switches to the light fixture on a ceiling fan. One switch is a Cooper over/under Duplex switch with the top being a single pole switch that controls the fan and a 3-way switch on the bottom for the light. The other side of the room has your standard 3 way toggle switch. Power is coming into the duplex switch side then to the fan/light and on to the 3 way toggle switch side. No problem with the fan switch. Below is how I wired the light. I can turn the light on and off at the right side switch (toggle) and then and only then can I turn off the light at the duplex switch (bottom 3 way). When I turn the light off at the right side switch (toggle), I cannot turn it on at the duplex. How can I rectify this situation without going from switch to switch to light? I wired the 3 way switch on the Duplex side the same as this attached diagram. Black wire from the right side 3 way toggle switch is attached to the blue/light wire in the fan.
I attached the white wire coming from the left side duplex switch side to the Common white wire on the fan, which I believe is common to the circuits for the entire fan.
[IMG]mailbox:///C:/Users/Glenna/AppData/Roaming/Thunderbird/Profiles/wp5ymoj2.default/Mail/pop.east.cox.net/Sent?number=1498013&part=1.2.2&filename=Large-3-way-switch-3.jpg[/IMG][IMG]mailbox:///C:/Users/Glenna/AppData/Roaming/Thunderbird/Profiles/wp5ymoj2.default/Mail/pop.east.cox.net/Sent?number=1498013&part=1.2.2&filename=Large-3-way-switch-3.jpg[/IMG][IMG]mailbox:///C:/Users/Glenna/AppData/Roaming/Thunderbird/Profiles/wp5ymoj2.default/Mail/pop.east.cox.net/Sent?number=1498013&part=1.2.2&filename=Large-3-way-switch-3.jpg[/IMG]http://www.homeimprovementweb.com/in...s/wiring3l.gif
rjniles 11-19-2012 06:50 AM
The diagram you show is correct, if if doesn't work:
You wired differently than the diagram
Or
You have a bad switch.
Check the terminals on the 3 ways and be sure you have correctly id'd the commons.
joed 11-19-2012 07:31 AM
What cable did you run between the double switch and the light? You need four wires + ground to make it work properly
rjniles 11-19-2012 07:56 AM
I do not see the need for a 4th wire. He shows the neutral connected to the light and the hot extended to the far end switch common. Plus the 2 travelers.
The need for a 4th wire would only be to comply with NEC 2011 and have a neutral in the far end switch box.
RAUL HIDALGO 11-19-2012 08:30 AM
most likely one of the travelers is miswired in rare ocasions its a faulty switch
oh'mike 11-19-2012 08:39 AM
If the push in 'back stab' holes were used---some times they don't line up with the colored screws---causing a miswired circuit
hammerlane 11-19-2012 09:49 AM
1 Attachment(s)
the diagram is correct...cannot say that about the wiring your location though.
The diagram below does not show ground wire for ease of drawing
joed 11-19-2012 10:13 AM
He has a second switch in the first box to control the fan. You need a fourth wire for that.
rjniles 11-19-2012 10:19 AM
Joed,
I assumed he was only showing us the wiring for the light. He did say "No problem with the fan switch".
Poster, did you run another cable for the supply to the fan?
Aurora65 11-23-2012 07:36 AM
Diagram on how to wire 2 - 3 way switches to a ceiling fan
I ran 14/2 wire to the first switch, 14/3 to the fan and also to the second/regular trip switch.
Aurora65 11-23-2012 07:38 AM
Thanks!! I will check my wiring again (4TH OR 5TH TIME) and I may also replace the 3-way trip switch as advised.
Aurora65 11-23-2012 07:40 AM
Or
I will completely go through my wiring of these switches and then swap out the last 3-way trip switch. I hope this works because I haven't been able to see the obvious.
Aurora65 11-23-2012 07:44 AM
Originally Posted by rjniles (Post 1055958)
Joed,
Yes I ran a 14/2 wire from the top single pole switch to the fan black wire. As I stated, the fan works just as it is supposed to with the single pole switch.
k_buz 11-23-2012 07:45 AM
Ok, lets get specific here...
You ran a 14/2 to the stacked switch.
You ran a 14/3 from the stacked switch to the fan box.
You ran a 14/3 from WHERE to the other switch box? This is the important information. If you ran this cable from the fan box to the 2nd switch box, then you will need another wire.
k_buz 11-23-2012 07:52 AM
I see you added some information. Do us a favor...post a list of each cable you used from where to where for both switches.