Determining Main Panel Load With Subpanel Added - Electrical - DIY Chatroom Home Improvement Forum
Old 04-11-2008, 12:15 PM   #1
Determining Main Panel Load with Subpanel added
Discussion in another thread got me thinking about a very important consideration when adding a subpanel to a main panel:
When adding a subpanel, does the load for the MAIN panel become the sum of the loads of both panels or is it calculated differently?
LOAD=Main+Sub
What if additional subpanels are added?
It seems that if you are adding subpanel to a MAIN because the MAIN is full, you would be taxing the load capacity of the main panel if you also filled the subpanel.
Randell Tarin is offline   Reply With Quote
Old 04-11-2008, 02:13 PM   #2
Electrician
Rewards Points: 760
You will not be overloading your main panel, your main panel would draw only as much as your main breaker can handle.
If your main panel is full and you add another subpanel, as long as you don't go over the rateing of the main breaker you are fine. You could have a full main panel as well as 10 subpanels that are all full but as long as you don't exceed the main breaker you will have no problems.
darren is offline   Reply With Quote
Old 04-11-2008, 02:21 PM   #3
Licensed Electrician
jrclen's Avatar
Rewards Points: 514
LOAD=Main+Sub
You are correct. If you are doing a load calculation for your service, you would add the service panel (main) loads plus the sub panel loads from all sub panels. Note, we are talking about actual loads and not merely adding up the sums of all branch over current devises.
jrclen is offline   Reply With Quote
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 08:40 PM
Replace main panel or use subpanel? MasterofNone Electrical 8 02-12-2008 01:24 AM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM
Connecting subpanel to main panel rtyui2 Electrical 10 12-07-2007 07:29 PM
Add subpanel or upgrade main panel dcoz Electrical 1 01-12-2006 10:24 AM