Detached Garage Sub Panel Questions - Electrical - DIY Chatroom Home Improvement Forum
Old 10-09-2010, 05:33 PM   #1
I am planning to run 240 out to my detached garage for a couple of power tools and I want to make sure it will be done properly. The run to the garage will be about 80' and after doing a lot of reading this is my plan:
1. Install a double pole 60 amp breaker in my main 100 amp panel for the run.
2. Use #6\3 UF Direct Burial wire in a 24" deep trench.
- Is this generally cheaper than running separate THWN wires in conduit?
- Do I need 6\3 wire with a ground even though I am running the ground from the sub panel to the grounding rod? Seems redundant.
3. Install a 60 amp sub panel without a main disconnect.
4. Install a #10 AWG copper ground wire to a separate 8' ground rod.
5. Make sure the ground and neutral bars are separated.
I will be running a 240v table saw quite a bit and a 240v welder on rare occasions. Other than that it will pretty much be 1 or 2 20amp plugs and the rest 15amp plugs and general lighting. Any advice or corrections would be much appreciated.
Thanks,
Scott...
smuth10 is offline   Reply With Quote
Old 10-09-2010, 05:58 PM   #2
Just call me Andrew
Rewards Points: 1,020
1. Install a double pole 60 amp breaker in my main 100 amp panel for the run. Yes
- Is this generally cheaper than running separate THWN wires in conduit? I would use THWN in conduit. I think most areas only require 18" of cover, but check your local code.
- Do I need 6\3 wire with a ground even though I am running the ground from the sub panel to the grounding rod? Seems redundant. The grounding rods do NOT provide means to trip a breaker if there is a short. They serve very different purposes, so it's not redundant. The ground rod(s) dissipate a lightning strike. The ground back to your panel trips the breaker if a hot wire touches something it shouldn't (like the frame of your saw).
3. Install a 60 amp sub panel without a main disconnect. I believe you need a local disconnect since it's a detached building. You can use any size breaker (60 or above) since the feed is already protected up to 60A.
4. Install a #10 AWG copper ground wire to a separate 8' ground rod. I think you need 2 grounding rods...I may be wrong though.
5. Make sure the ground and neutral bars are separated. Yes, test with a continuity tester if not sure.
Andrew
secutanudu is offline   Reply With Quote
Old 10-10-2010, 08:26 AM   #3
Thanks for the quick reply secutanudu.
So you don't think 6\3 wire is too small for that long of a run?
As far as the sub panel is concerned, I am a little fuzzy. I will check my local code to find out if it needs a disconnect or not, but why would I be able to put in a 100 amp disconnect breaker in the sub panel when there is only a 60 run out there?
Also, why do the ground and common bars need to be separated in this situation? I read they need to be, but have no idea why. In my main panel this is a bar coming across attaching the two.
Thanks again, Scott...
Old 10-10-2010, 09:01 AM   #4
Licensed electrician
Rewards Points: 1,622
You can reference these stickies for subpanel installation.
http://www.dropshots.com/stubbie4#al...0Installations
The 100 amp at the outbuilding would just act as a disconnect.
Old 10-10-2010, 09:11 AM   #5
I=E/R
a7ecorsair's Avatar
#6 UF in copper is listed as 55 amps
#6 THWN in copper is listed for 65 amps
because the 60 amp breaker in the main panel will protect the wire to 60 amps.
a7ecorsair is offline   Reply With Quote
Old 10-10-2010, 09:44 AM   #6
Thanks for those drawings. It clears things up for me and I can get started. One last question of course. Can I buy a small 100 amp panel for the garage and then use a 60 amp breaker for the main breaker? I guess I don't understand being able to run a 60 amp service out from the main and then use a higher rated breaker out at the garage.
Thanks, Scott...
Old 10-10-2010, 10:17 AM   #7
I=E/R
a7ecorsair's Avatar
Thanks, Scott...
Think of this way. A light switch in your house turns a light on and off but the breaker protecting the wires is in the panel. The 100 amp breaker that would be in your garage will turn the garage on and off but the breaker protecting the wires from the main to the garage is protected by the 60 amp breaker. The individual circuits in the garage are protected by those individual breakers.
Old 10-10-2010, 11:27 PM   #8
Just call me Andrew
I had the same question...
Why can't you connect Ground/Neutral bus bars on a sub
Andrew
Old 10-11-2010, 11:24 AM   #9
"4. Install a #10 AWG copper ground wire to a separate 8' ground rod. "
Your grounding electrode conductor (the conductor that attaches to your electrode, which is a ground rod in your case) needs to be #8 minimum. I know this may be confusing since you only needed a #10 for the equipment grounding conductor from your main panel, but #8 is the required size from Table 250.66 in the NEC. Good luck
DetroitEE is offline   Reply With Quote
60 amp sub panel for a detached garage canyonbc Electrical 32 01-11-2010 11:53 AM
wiring 100A to detached garage snowman Electrical 4 11-28-2009 04:53 PM
100 -> 200 amp panel upgrade questions philipjcaputo Electrical 1 10-30-2009 03:35 AM
Enhancing existing wiring to detached garage justinperkins Electrical 46 07-07-2008 07:29 PM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM