ifinew
detached garage
I could use some pro help, i have been lurking around here searching a bit
it have an existing 1.5" ent buried between house and garage with no known metalic connection.
i would like to know what size power conductors can be used through it and be within the fill/%.
after looking in the lb's i need to change out nmb6 with something else.
also need info on distance of a ground rod from the breaker box inside.
it needs an upgrade on the electric for a welder and some correcting.
i have purchased a square d homline mainlug 125 box 8 space but my most recent search ( garage box cannot be between studs? has to be outside of sheetrock?)
brmax is offline   Reply With Quote
Old 05-10-2008, 03:56 PM   #2
If it's emt (thinwall)....it's probably all rotted out......thinwall is not rated for burial.
Joba Fett is offline   Reply With Quote
Old 05-10-2008, 07:22 PM   #3
ifinew
conduit
Its the pvc type gray in color 1.5", the run length is 56' from box to box 1 way
im wanting to know if #2 or #4 can be used for the two hots and if the neutral has to be the same size. i understand the green to ground rod can be smaller.
are these wires to big for this existing conduit?
Old 05-10-2008, 07:29 PM   #4
electrical contractor
Rewards Points: 150
Joba, I believe the post says ENT Electrical Nonmetalic Tubing. Is this correct brmax? If this is the case you can pull 3 #3awg THHW and 1 #6 THHW, this will get you a 100 amp feeder to your sub panel. Hook the wires on a 100 amp breaker in your main panel, use the #6 for the ground, because this is a sub panel you must run a 4 wire feeder to the sub. In the sub do not bond the neutral to the ground, and do not mix the neutral and ground conductors for the branch circuits.
Jimmy
Life is tough, Life is tougher when you are stupid.
wire_twister is offline   Reply With Quote
Old 05-10-2008, 07:30 PM   #5
Idiot Emeritus
Rewards Points: 1,492
If it is indeed ENT (electrical nonmetallic tubing), the codebook says in table C.1(A) that four 2/0 thhn/thwn will fit. In reality though, if it's longer than about 10' and has more than 1 90 in it, it'd be a royal bear to pull.
If it's schedule 40 PVC, according to table C.10(A), four 1/0,s are allowed. Again, a hard pull.
Realistically, depending on length and number of 90's, three #2's and a ground wouldn't be too difficult to pull in. That's good for 100 amps.
Rob
micromind is offline   Reply With Quote
Old 05-10-2008, 07:36 PM   #6
Rewards Points: 150
It is # 2 and not #3 good catch Rob thanks. brain death is a terrible thing!
Jimmy
Old 05-11-2008, 09:22 AM   #7
ifinew
conduit
thanks for the replys, so i understand this heres whats on the pipe
1 1/2 sch 40 rigid pvc conduit max 90 deg c wire nema tc2 sunlight resistant 98 may 26 2 3 ba s e126014 underwriters labratories inc listed nonmetalic conduit above ground and below ground # u649
getting the old out doesnt look that easy thought about picking up some grease lookin stuff i seen at graybar and putting down the lb access.
anyway the hook up to main panel or meter is what im after at this time
do i have to run a 4 wire ? its detached, i thought instaling a ground rod was the deal, new nema 08 ok
i still cannot understand not being able to flush mount the breaker box can anyone explain this
Detached Garage Sub Panel Grounding Q integlikewhoa Electrical 15 03-12-2015 07:02 PM
Mold in detached garage jkrodger Building & Construction 15 05-01-2009 01:46 PM
detached garage Kapt Electrical 12 01-17-2007 08:37 AM
Best way to insulating a heated detached cement block garage Joe Nulph Building & Construction 1 03-06-2006 10:30 AM
Detached garage adding a 3 way switch. Slatherd Electrical 4 01-02-2006 02:53 PM