Delta Table Saw Trips GFCI - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 04-09-2010, 06:40 PM   #16
The starting capacitor does not increase or decrease the amount of current flow, it does however cause a time shift in the flow from the hot to the neutral and the neutral to the hot. The time shift means that at a given time the current flow on the hot is different than the current flow on the neutral. A difference of current flow between the hot and neutral side is what causes the GFCI to trip.
hayewe farm is offline   Reply With Quote
Old 04-10-2010, 05:37 PM   #17
For troubleshooting purposes you could try running the saw from the GFCI through a #14 or #12 extension cord. This should reduce the startup surge somewhat.
For a 15A saw and a 5% voltage drop at 120v max lengths would be 75' and 125', respectively.