Dedicated Ciruit for AC and single receptacle...
Just want to make sure it is ok to use single receptacles on my dedicated cirucits for my ACs. I have 3 in wall units all on their own circuits. 1 20A and 2 15A circuits.
Should they all have the single receptacles as in the image? Or does it matter?
zephed666 is offline
Old 05-02-2013, 01:50 PM   #2
Your picture is of a 15A receptacle. This is acceptable for the 15A circuits. If you have only a single receptacle on a branch circuit (not a duplex receptacle), the rating of the receptacle needs to match the rating of the circuit. You would need a 20A receptacle for the 20A circuit, or change the breaker to 15A.
This assumes, of course, that all of the wiring is properly sized for the individual circuits.
Also, the image is not a tamper-resistant receptacle. Depending on your code cycle, you might need TR receptacles (I think they are a good idea regardless of the code cycle).
clashley is offline
Old 05-02-2013, 02:07 PM   #3
Rewards Points: 172
I just grabbed the pciture for an example. I have the correct receptacles on the lines. Not TR though.
Just wanted to make sure that ehy could be single. Can you put a duplex on there or bad idea?
Old 05-02-2013, 02:16 PM   #4
JW
mm11's Avatar
Rewards Points: 596
If a duplex receptacle is used, the circuit is no longer an individual branch circuit.
There could be another cord and plug connected load, in addition to the A/C load, if using a duplex.
mm11 is offline
Old 05-02-2013, 02:17 PM   #5
Rewards Points: 172
So stick with the single receptacles? I just wanted to make sure it's right.
Old 05-02-2013, 02:28 PM   #6
jproffer's Avatar
Rewards Points: 706
I'd stick with the single, just remember (as clashley said) you'll have to use 20A receptacles on the 20A circuits....but it sounds like you've already got that covered.
jproffer is offline
Old 05-03-2013, 10:36 PM   #7
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
a 20 amp circuit can use either a 20 outlet or and 15 amp outlet ...
a 15 amp circuit can only use a 15 amp outlet ...
nec Table 210.21(B)(3)
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline
Old 05-04-2013, 01:56 AM   #8
Rewards Points: 512
nec Table 210.21(B)(2)
210.21 (B) (1). Regarding the use of singles, requires a receptacle not less than the branch circuit??
Edit: which means that a 15-a Single cannot be put on a 20a circuit.
Installation is the Reverse of Removal.
sirsparksalot is offline
The Following User Says Thank You to sirsparksalot For This Useful Post:
Philly Master (05-04-2013)
Old 05-04-2013, 06:30 AM   #9
Rewards Points: 516
Originally Posted by sirsparksalot View Post
210.20 (B) (1). Regarding the use of singles, requires a receptacle not less than the branch circuit??
Table 210.21(B)(2) ..
and ... I do not have the book here inside and i cannot find 210.20(B)(1) i could only find .. 210.20(B)
(B) Conductor Protection. Conductors shall be protected in accordance with 240.4. Flexible cords and fixture wires shall be protected in accordance with 240.5.
you may have meant 210.21 (B) (1)
anyway all the more reason to use a Duplex outlet but it would need to comply with ...210.23(A)(2)
210.23 Permissible Loads. In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.
(A) 15and 20-Ampere Branch Circuits. A 15or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2).
Exception: The small-appliance branch circuits, laundry branch circuits, and bathroom branch circuits required in a dwelling unit(s) by 210.11(C)(1), (C)(2), and (C)(3) shall supply only the receptacle outlets specified in that section.
(1) Cord-and-Plug-Connected Equipment Not Fastened in Place. The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branchcircuit ampere rating where lighting units, cord-and-plugconnected utilization equipment not fastened in place, or both, are also supplied.
The Following User Says Thank You to Philly Master For This Useful Post:
sirsparksalot (05-04-2013)
Old 05-04-2013, 07:33 AM   #10
Rewards Points: 730
Originally Posted by gregzoll View Post
That outlet is acceptable on a 20amp circuit.
That receptacle is not acceptable on a 20A circuit if it is the only outlet on the circuit, as was asked by the OP.
Mark
busman is offline
The Following 3 Users Say Thank You to busman For This Useful Post:
electures (05-05-2013), Jim Port (05-04-2013), stickboy1375 (05-04-2013)
Old 05-04-2013, 07:44 AM   #11
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
That outlet is acceptable on a 20amp circuit. You just cannot put a 20 amp outlet on a 15 amp circuit, due to if someone plugged in a 20 amp appliance with the side turned prong, it would overload the 15 amp breaker, and trip it.
If it is an individual branch circuit and using a single receptacle, then he can use a 20amp receptacle on a 15 amp protected circuit.
stickboy1375 is offline
The Following User Says Thank You to stickboy1375 For This Useful Post:
Old 05-04-2013, 09:37 AM   #12
Licensed electrician
Rewards Points: 1,266
From 210.21 for individual receptacles.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit
shall have an ampere rating not less than that of the branch
circuit.
Exception No. 1: A receptacle installed in accordance
with 430.81(B).
Exception No. 2: A receptacle installed exclusively for the
use of a cord-and-plug-connected arc welder shall be permitted
to have an ampere rating not less than the minimum
branch-circuit conductor ampacity determined by 630.11(A)
for arc welders.
(B)(1) would allow the use of a 20 amp slot receptacle on a 15 amp circuit.
Jim Port is offline
The Following 4 Users Say Thank You to Jim Port For This Useful Post:
busman (05-04-2013), electures (05-05-2013), sirsparksalot (05-04-2013), stickboy1375 (05-04-2013)
Old 05-04-2013, 10:16 AM   #13
E2 Electrician
Unless of course were talking about a single receptacle and a individual branch circuit.
Old 05-04-2013, 05:45 PM   #14
Rewards Points: 516
OP asked a second question ..post #3 ..in addition to the first one ....
I should have "quoted" it in my response sorry for the CORNfusion ....
Old 05-04-2013, 06:40 PM   #15
E2 Electrician
Yes, and you can use 20 amp single receptacles on all (3) units.
Closed Thread
3 way, 4 way, Single Pole/3-Way Combinations slash5bmw Electrical 5 06-22-2010 08:21 AM
Replacing duplex receptacle with nighlight - wiring question Rabu Electrical 6 05-02-2010 08:51 PM
Three hot wires coming into a receptacle? Jeff DIY Electrical 10 10-07-2009 02:35 PM
Wiring A Ceiling Fan, Receptacle, and Outside Light merlin6984 Electrical 9 03-26-2009 10:52 PM
single gang single pole switch on fan fabian Electrical 14 03-05-2009 02:11 AM