I'm installing a whirlpool type tub that requires two 15a GFCI protected circuits. One for the pump and one for the heater. I want to use blank faced GFCI outlet that will be located in an adjacent closet.
-Can both of these circuits enter a common 2 gang outlet box and get wired to a split receptacle since both circuits are running to the same location if all wires are kept separate besides the ground?
-Is there a problem in running electrical cable past plumbing lines?
RalphPeters is offline   Reply With Quote
Old 02-17-2011, 04:58 PM   #2
Master Electrician
Rewards Points: 3,966
You will need separate GFCIs for each circuit.
brric is online now   Reply With Quote
Old 02-17-2011, 05:01 PM   #3
Rewards Points: 79
Yes I plan on using two two blank faced GFCI's. Can they be mounted in a two gang box, same thing with the outlet box?
Old 02-17-2011, 05:01 PM   #4
Electrical Contractor
kbsparky's Avatar
To answer the OP, YES!
You can mount both blank-faced GFCI units in a 2-gang box, and then feed a split-wired outlet under the tub.
Be sure to remove both interconnection tabs on the split-wired outlet.
-KB
Old 02-17-2011, 05:03 PM   #5
Rewards Points: 79
OK Thanks.
So no problem with plumbing lines and electrical cable?
Old 02-17-2011, 05:05 PM   #6
Electrician
Rewards Points: 802
If you do this you will need to bring 2 two wire cables to the plug and break off each side of the plug. If you run a 3 wire you will have nuiance tripping of the GFI.
darren is offline   Reply With Quote
Old 02-17-2011, 05:06 PM   #7
kbsparky's Avatar
I'd use a 4-wire cable. Do that have that available in Canada?
As long as you don't install the wires inside of those plumbing pipes, you should be good to go.
-KB
Old 02-17-2011, 05:11 PM   #8
Rewards Points: 79
I was planning on running two 14-2 cables but if I can run just one cable from the breaker box it makes it a lot easier.
Old 02-17-2011, 05:31 PM   #9
Electrician
Rewards Points: 802
You can use a 14/3 from the panel to the GFCI as long as you pigtail the neutral at them. From the GFI you will need two 14/2 to the plug. I have never seen 4 wire lomex but you can get 4 wire BX, if you get 4 wire BX techincally you would have to derate because you have more then 3 current carrying conductors. So for a 15A breaker you would have to use 12/4.
Old 02-17-2011, 06:22 PM   #10
The easiest way to do this is, run 2 separate 14/2 , always a good
Idea not to share neutral when running two motors, put the GFI's at the panel (easy to reset if GFI trips) then run your individual 14/2 to regular plugs near your tub or wherever u were going to put them. Keeping the motors separate, by running 2-14/2's is good if there's ever a problem with either the pump or heater, easy to figure out which is having trouble if it was to have own feed
Jeter is offline   Reply With Quote
Old 02-19-2011, 08:49 AM   #11
I have to agree with brric depending on the draw of the tub and the heater I would have a seperate GFI for each one and each would be a 20 amp line right under the tub with an accessible door.
SPINA ELECTRIC is offline   Reply With Quote
Old 02-22-2011, 04:21 PM   #12
Rewards Points: 79
It seems that all faceless GFCI's are rated at 20 amp. Is that OK on a 15 amp circuit?
http://www.leviton.com/OA_HTML/ibeCC...minisite=10026
Specs say :
General Information
GFCI ratings:
15A-125V AC - Cat No. 7599 Duplex
Receptacle
20A-125V AC - Cat. No. 7590 Faceless
20A-125V AC - Cat. No. 7899 Duplex
Receptacle
All devices rated 20A feed-through
Old 02-22-2011, 04:34 PM   #13
Master Electrician
No problem.
Old 02-22-2011, 05:14 PM   #14
Rewards Points: 79
dedicated circuit for table saw MeanGene Electrical 6 11-03-2010 08:31 PM
Planning circuit layout for barn tbeaulieu Electrical 8 04-08-2010 09:38 AM
Moving a Fridge, is a dedicated circuit required...or not? Snowy334 Electrical 7 07-03-2009 12:36 PM
Dedicated 20amp circuit chingon Electrical 1 03-31-2009 06:36 PM
Circuit advice for finishing basement Straightgrain Electrical 16 03-25-2009 09:07 AM