Dead Slots In QO Sub Panel?? - Electrical - DIY Chatroom Home Improvement Forum
Old 09-10-2011, 09:57 PM   #1
Angry
Dead slots in QO sub panel??
OK OK OK I think I finally have my sub panel wired correctly for switching between green power and grid power. Problem now is i, seemingly have 2 dead slots out of 4 in the panel. I can get two to work correctly but the other two are not putting out anything.....Its a Square D QO generator subpanel (4 space). Anyone have any ideas??
:furi ous:: censored:
Rayhay72 is offline   Reply With Quote
Old 09-10-2011, 09:59 PM   #2
Licensed electrician
Rewards Points: 1,028
I think in your other thread you said you were feeding this panel with 120 or only one hot leg. This will leave every other slot dead.
Rayhay72 (09-10-2011)
Old 09-10-2011, 10:13 PM   #3
Sparky
Rewards Points: 510
you need a tap for 3 #6's, put a short length in each lug in the sub panel, then take both of those and tie it to your incoming 120v feed
Techy is offline   Reply With Quote
The Following User Says Thank You to Techy For This Useful Post:
Old 09-10-2011, 10:30 PM   #4
Code05's Avatar
Rewards Points: 1,104
Not sure of exactly what you are saying, But if you are saying a double tap, generally that is a no go.
110.14(A) Terminals. Connection of conductors to terminal parts
shall ensure a thoroughly good connection without damaging
the conductors and shall be made by means of pressure connectors
(including set-screw type), solder lugs, or splices to
flexible leads. Connection by means of wire-binding screws or
studs and nuts that have upturned lugs or the equivalent shall
be permitted for 10 AWG or smaller conductors.
Terminals for more than one conductor and terminals
used to connect aluminum shall be so identified.
408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor.
Code05 is offline   Reply With Quote
The Following User Says Thank You to Code05 For This Useful Post:
Old 09-10-2011, 10:42 PM   #5
Sparky
Rewards Points: 510
i'm saying he needs something like this to split his one incoming 120v feed to 2 wires to land one on each buss
Old 09-10-2011, 10:51 PM   #6
Depending on the size of the incoming feeder the OP might be able to use wire nuts with 2 pigtails.
Old 09-11-2011, 04:06 PM   #7
Wow I feel dumb....
Thanks guys,
This install has really kicked my butt and taxed my abilities as handyman and or electrician. Obviously I am neither. Been working on this mess for near 3 months and finally ( i think ) got it all together.
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 08:15 PM
Garage Sub Panel Questions mscanlon01 Electrical 3 07-20-2011 11:03 AM
200A upgrade and move, backfeeding permitted? WillK Electrical 3 05-30-2011 09:00 PM
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 08:40 PM
Melted Service Entrance Wire in Panel theatretch85 Electrical 13 08-22-2008 11:37 AM