DC Amps Wire Sizing - Electrical - DIY Chatroom Home Improvement Forum
Old 06-13-2011, 05:40 AM   #1
DC amps wire sizing
Do DC amps need to be rated to 80% of the circuit breaker size like AC amps do?
I have a marine battery charger that needs + and - cables but dont know what size wire I need, the charger has an output of 12v 15A DC. so with the 80% value I'd need the next wire size up which is 12gauge @ 20A. Is this correct? it seems like like its really small wire compared to actual real jumper cables
bluemoonshine is offline   Reply With Quote
Old 06-13-2011, 05:57 AM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
Where did you hear this myth???
You have a charger, not jumper cables. BIG difference.
#14 or #12 will be fine for what you are doing. Unless of course the length is pretty long, like over 50'.
Old 06-13-2011, 06:13 AM   #3
What he said. Jumper cables are required to carry a LOT of current for a very brief time span. Not the same set of requirements for a charging circuit.
Old 06-13-2011, 07:49 AM   #4
I=E/R
a7ecorsair's Avatar
Ever look at the cables that connect to your car battery? They are probably #4 copper stranded wire. That is because when you energize the starter motor, especially in cold weather, it draws lots of current - maybe even a 100 amps. Jumper cables have to support this current draw too. For your charger use #14 stranded wire, it will be fine, and #14 rip cord is a good choice. When you charge a battery it only draws heavily for a short time and then the current will taper off as the battery charges.
a7ecorsair is offline   Reply With Quote
convert 3 wire range junction box to receptacle filby Electrical 0 06-05-2011 01:33 AM
Box fill and wire nuts zephed666 Electrical 7 05-02-2011 12:51 PM
HVAC three wire motor to six wire motor Leo Caproni HVAC 5 10-18-2010 01:23 PM
Max amps allowed - electrician advice needed Des Electrical 27 06-05-2008 10:31 PM
Wire sizing rtyui2 Electrical 4 04-21-2008 04:29 PM