Dayton 1 1/2 Hp 3 Phase Motor - Electrical - DIY Chatroom Home Improvement Forum
Old 10-11-2012, 01:48 PM   #1
dayton 1 1/2 hp 3 phase motor
does not have reverse rotation wiring diagram on it. can I reverse this motor if it dosen't come with a ccw wire hookup on it?
bongojim is offline   Reply With Quote
Old 10-11-2012, 02:44 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 548
To change rotation on a 3 phase motor, swap L1 with L3.
jbfan is online now   Reply With Quote
Old 10-11-2012, 03:06 PM   #3
dayton 1 1/2hp 3 phase
my wires are in a series as follows coming in from my inverter. T7-T1, T8-T2, T9-T3. When swapping any 2 of these to try to reverse my motor, all my motor does is hum. the other wires coming from the motor tied together are T4-T5-T6. This is considered low voltage connection on the motor.
Old 10-11-2012, 03:14 PM   #4
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
I think you misunderstood.
L1 to T1&T7
L2 to T2&T8
L3 to T3&T9
T4-T5-T6 together.
Switch L1 & L3
Now it should be L1 to T3&T9, L3 to T1&T7, L2 to T2&T8
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
jbfan (10-11-2012)
Old 10-11-2012, 03:22 PM   #5
just got the motor running in reverse. i misunderstood what you were telling me at first, but realized I was switching the wrong wires. when I switched the power leads going into the dayton motor it reversed. thank you for your help.
Old 10-12-2012, 01:01 AM   #6
Semi-Pro Electro-Geek
Rewards Points: 2,970
If you have an inverter (VFD) operating the motor, you can probably reverse it from the inverter. Every VFD I have seen will run either direction.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is online now   Reply With Quote
How to replace condensor fan motor? twags HVAC 44 08-27-2015 05:09 PM
hELP! Amperage needed for 220V motors 1488rob Electrical 36 01-28-2014 04:44 PM
Sizing Motor Branch Circuit Conductors and OCPD's electures Electrical 5 06-22-2011 11:32 PM
dayton fan motor Turk Electrical 1 02-27-2009 05:38 PM
Replacing a Condenser Fan Motor thothtp HVAC 5 06-08-2008 06:30 PM