Cracked Circuit Breaker - Electrical - DIY Chatroom Home Improvement Forum
Old 05-18-2012, 01:54 AM   #1
Rewards Points: 243
My 90A double-pole full width GE circuit breaker casing is cracked. It starts at the handle opening and runs down one side to the base, moving away from the bus stabs and towards the wire terminals, as far as I can tell without removing it from the panel. Should I consider this an urgent replacement, or can I swap it out next time I'm doing work in the panel?
chemman is offline   Reply With Quote
Old 05-18-2012, 05:16 AM   #2
Rewards Points: 1,300
We would need a picture, but I doubt it is cracked. Most of the double pole breakers are two single pole breakers riveted together and Handle tied.
danpik is offline   Reply With Quote
Old 05-18-2012, 07:04 AM   #3
Electrical Contractor
jbfan's Avatar
Rewards Points: 552
If it is indeed cracked, you need to replace it right away!
jbfan is online now   Reply With Quote
The Following 2 Users Say Thank You to jbfan For This Useful Post:
Code05 (05-18-2012), rrolleston (05-18-2012)
Old 05-18-2012, 12:11 PM   #4
Rewards Points: 243
Does that clear it up? And I was wrong about the location of the crack, it runs right along the corner toward the bus stabs. Guess my memory isn't so great in the middle of the night, huh?
Old 05-18-2012, 12:35 PM   #5
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
I would replace it now. And I would turn the main off when removing the old breaker.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 05-18-2012, 12:36 PM   #6
Code05's Avatar
Rewards Points: 1,104
I would replace that one ASAP.
Code05 is offline   Reply With Quote
Old 05-18-2012, 01:33 PM   #7
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Seeing this small picture, I am curious what the rest of the panel looks like.
Old 05-18-2012, 03:14 PM   #8
Sparkaholic
Rewards Points: 150
Send a message via Yahoo to sparks1up
The breaker should be replaced soon but it also doesn't look like 90-amp rated wiring coming off that breaker? Looks like #6, maybe #4 but still not 90-amp rated.
Answers based on the mood I am in when you ask!
sparks1up is offline   Reply With Quote
Old 05-18-2012, 05:24 PM   #9
Rewards Points: 243
Crap, I should have rotated it. The wiring going to the 90A breaker is #4 AWG 3 conductor and is feeding my air handler which contains my emergency heater banks. The air handler has two double pole breakers on the front, a 30A and a 60A. I'm curious as to the comments on the panel.
Old 05-18-2012, 05:31 PM   #10
Sparkaholic
Rewards Points: 150
#4 cable is only rated for 70-amps
Old 05-18-2012, 05:45 PM   #11
Rewards Points: 243
I thought #4 was good for 90A at 90C. Of course I'm assuming that circuit is entirely rated for 90C. Of course this will mean the new circuit breaker will be even more expensive.
Old 05-18-2012, 06:03 PM   #12
k_buz's Avatar
#4 THHN is rated for 85 Amps, at 70 degrees. Since the next standard size breaker is 90A you can use a 90A breaker.
That doesn't look like #4, looks like #6 THWN.
Old 05-18-2012, 06:12 PM   #13
Sparkaholic
Rewards Points: 150
For cable/romex you use the TW column in 310.16
#6 (cable/romex) = 55-amp and #4 (cable/romex) = 70-amps
#4 THWN = 85-amps
Old 05-18-2012, 06:20 PM   #14
k_buz's Avatar
You are correct...I don't equate #4 and NM...in fact, I've never even seen 4-3 NM cable.
And come to think of it, if the 6-3 shown in the picture is fused at 60A or less on the other end, it being on a 90A breaker in this panel is of no concern.
Old 05-18-2012, 09:58 PM   #15
rrolleston's Avatar
They make up to 2-3 NM-B romex but it's a bear to work with.
New wiring tripping breaker on another circuit? Kinggofg Electrical 11 04-26-2012 01:36 AM
Backfeed Circuit Breaker Knucklehead_BW Electrical 13 01-11-2012 09:17 PM
circuit breaker? blueandyellow Electrical 7 01-30-2011 10:27 PM
Circuit BReaker Question - breaker didn't trip and no power thru the circuit Ronin_67 Electrical 2 08-08-2008 06:06 AM
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 05:55 AM