Correct Wiring To Subpanel In Garage - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 01-17-2013, 09:28 PM   #16
Doityesterday
Send a message via Yahoo to papachuck
Are you all set now? A stupid question is one that is not asked do not assume when it comes to electric. if your sub panel already has A common ground bar and your using 4 wires. hook one ground wire size #2 to neutral buss bar and the other ground left to the ground bar. this is were all your bare grounds go and neutral white wires go on the buss bars.
papachuck is offline   Reply With Quote
Old 01-17-2013, 09:30 PM   #17
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
No he is not all set SER cable is not rated for underground use.
338.12 Uses Not Permitted.
(A) Service-Entrance Cable. Service-Entrance Cable (SE) shall not be used under the following conditions or in the following locations.
(2) Underground with or without a raceway
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 01-17-2013, 09:30 PM   #18
grounding recommendations-
Papachuck-
thanks for your suggestions... yes the house has 2 rods and #6 CU. planning on doing the same at the shop/garage. 2 copper ground rods, connected to the ground bus in the subpanel box and bonded to the frame. and correct I have to buy something to make a ground bus... I can see the raised bumps and screw holes in the subpanel frame where the busses go in. and just to be clear, you said in your earlier reply that the feeder ground connects with the neutral bus in the subpanel?
benjeremiah is offline   Reply With Quote
Old 01-17-2013, 09:57 PM   #19
Doityesterday
ok I see you still have the wrong wire . to make it simple you need 100amp UF direct underground .tell me if you plan on using 3 or 4 wires from main house.
Old 01-17-2013, 09:59 PM   #20
Doityesterday
your right my bad missed that thank you.
Old 01-17-2013, 10:04 PM   #21
Licensed electrician
Rewards Points: 1,266
Square D panel do not use that arrangement of bus bars. The ground bus is an additional purchase item. They mount on raised bumps on the back of the panel.
Old 01-17-2013, 10:08 PM   #22
Doityesterday
your right there but not if he purchased or picked it up from someone that had already installed one.
Last edited by papachuck; 01-17-2013 at 10:10 PM. Reason: A picture tells A thousand word's
Old 01-17-2013, 10:47 PM   #23
Missouri Bound's Avatar
He does not have a choice. All sub-panel feeds must be 4 wire.
Do you want it your way or the right way?
Old 01-17-2013, 11:18 PM   #24
Doityesterday
thank you but don't read just the last comment read up.was just making sure what he intended on doing.but again thanx
Wiring garage outlets from a subpanel ACR_SCOUT Electrical 24 12-01-2012 06:27 PM
Detached Garage Wiring elpht_man Electrical 5 09-23-2011 07:31 AM
wiring from existing panel to new garage al99m Electrical 8 07-29-2009 09:42 PM
Critique my wiring plan for my garage tigereye Electrical 10 03-24-2009 10:55 PM
Yet another garage subpanel thread (w/ pictures!) MattOverMinder Electrical 9 07-25-2008 03:15 PM