westbank 10-25-2012 11:06 AM
Hi,
I want to install a low voltage thermostat to control a fan-forced heater (5000W). I will need to install a relay and I wanted to make sure my wiring is correct.
I will go with the following relay:
Product page: http://www.aubetech.com/products/pro...=42&noLangue=2
Install manual: http://www.aubetech.com/manuel/2/RC840T.pdf
Here's my wiring diagram:
http://imageshack.us/a/img24/5512/wiringrelay.jpg
joed 10-25-2012 11:18 AM
Based on the manual link you have it wrong. You need to swap the blue and red wires coming out of the stat. The blue and black need to go to the line coming in.
westbank 10-25-2012 12:27 PM
Like this:
http://imageshack.us/a/img845/1579/wiringrelay2.jpg
mpoulton 10-25-2012 12:30 PM
Your wiring will cause a dead short across the incoming power when the thermostat turns on. Not good - will probably kill the relay. Switch blue and red, as joed says.
biggles 10-25-2012 12:46 PM
connect one line feed thru the N.O. contacts on that relay so the stat closes that N.O. to cycle the heater
westbank 10-25-2012 02:12 PM
Thanks for the advice. So my second wiring diagram is correct ?
mpoulton 10-25-2012 02:55 PM
Looks like it, yes.
joed 10-25-2012 06:21 PM
Yes second diagram looks correct.