Copper Wire Sizing Underground 185ft Run 200A Service - Electrical - DIY Chatroom Home Improvement Forum
Old 03-04-2009, 12:41 PM   #1
Copper wire sizing underground 185ft run 200A service
I live in Northern California and I want to install an underground service to a new construction, distance from power drop panel to sub panel is 185feet.
I have been told that for a 200Amp service the wire size will have to be 4/O Copper.
My question is: Can I use a smaller size Copper wire than 4/0 for the Ground conducter. Or do I have to run all three at 4/0?
It will be a standard 3 wire install through 3 inch Conduit.
Many thanks for any advice
DIYALLTHETIME is offline   Reply With Quote
Old 03-04-2009, 12:58 PM   #2
The 3 feeders must be 4/0 the ground the 4th wire should be #4
craneservice is offline   Reply With Quote
Old 03-04-2009, 01:26 PM   #3
Many thanks for such a quick reply
Do I have to run 4/0 copper as two hot legs, and one neutral, plus a ground leg from the 200A panel ( 4 wires total running to the home in 3" conduit) or can I run two 4/0 legs and one ground to the home if so what size ground and how would you then install this in the panel.
I have seen this in the past but I'm now a little unsure from your reply
Will I get a 240V supply at the house with a 3 wire pull, 2 hot legs 4/0 one ground 2/0? which can be used as a neutral? what are the complications of 3 wire or benefits of 4 wire install?
It will be a standard 240V single phase install through 3 inch buried Conduit.
Old 03-04-2009, 07:35 PM   #4
Idiot Emeritus
Rewards Points: 1,492
The minimum code size for a neutral is pretty small.
If it were me, I'd run the two hots as 4/0, and a 2/0 or maybe 3/0 for the neutral. #4 for the ground will be OK.
Rob
micromind is offline   Reply With Quote
Old 03-04-2009, 07:40 PM   #5
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Based on what?
Jamie
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 03-04-2009, 08:22 PM   #6
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
I think you mean 4/0 aluminum not copper...
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Remodel - Moving from 200 amp service to 320 amps stevedar Electrical 20 11-29-2009 08:14 PM
Melted Service Entrance Wire in Panel theatretch85 Electrical 13 08-22-2008 10:37 AM
Use a reduced neutral on 200a UG service ?? bradsguns Electrical 3 06-09-2008 08:00 PM
code for underground service tom b Electrical 6 10-10-2007 11:48 AM
200 amp panel with a 100 amp service? alexz Electrical 10 07-29-2007 10:00 PM