Old 01-12-2012, 05:01 PM   #1
011010100110111101100101
continuous load
When I was in school back in the early 90s, the continuous load allowed for a circuit per NEC was 80% duty cycle.
I've always gone by the 80% rule since, although I can't remember if it was a rule (shall) or under workmanship (should).
I've got a situation where I have two devices, both pulling 8.3 amps @ 240v and I'd love to put them on one circuit (20A double pole, 12awg), but that would put me at 83%. The total circuit length is under 75 feet.
I briefly flipped through the NEC and couldn't find it, and thought I'd ask if someone off hand recalls ?
-- Joe
anesthes is offline   Reply With Quote
Old 01-12-2012, 05:03 PM   #2
MarginallyQualified
continuous load
do those loads normally cycle simultaneously?
Old 01-12-2012, 05:04 PM   #3
Julius793's Avatar
continuous load
-- Joe
What kind of load?
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Old 01-12-2012, 05:16 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
continuous load
Not everything is a continuous load. Many people flat out put an 80% limit on a circuit, which is wasteful sometimes.
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
gregzoll (01-12-2012), J. V. (01-14-2012)
Old 01-12-2012, 06:56 PM   #5
continuous load
Continuous duty is over 3 hrs. Not 80%
bobelectric is offline   Reply With Quote
The Following User Says Thank You to bobelectric For This Useful Post:
Old 01-12-2012, 06:57 PM   #6
continuous load
Hi Guys,
I usually size my circuits this way (80%).
In this case, it's two electric heaters with fans. Mfg. specs say 8.3 amps each. Doesn't specify if that is peak or rms.
Most likely, both units would be on at the same time. Unsure of start up surge, have not even ordered them yet.
http://www.marleymep.com/en/multimed...-11046-001.pdf
-- Joe
Old 01-12-2012, 06:58 PM   #7
continuous load
Eh? We were taught 80%.
Looks like this changed a number of years ago:
http://forums.mikeholt.com/showthread.php?t=135362
Hrmm..
So it's 80% of the CB, not the circuit. If the breaker is 125% (will have to look at the specs) the cont. load is actually 20amps, but obviously if it's 100% it's 16 amps.
-- Joe
Old 01-12-2012, 07:10 PM   #8
continuous load
Come on, kids.Art.100,definitions... Continous loads.
Old 01-12-2012, 07:23 PM   #9
continuous load
deleted
The disadvantages of crab apple trees. In summer, the apples are too sour to pick and eat. In winter the birds come and leave dropping all over the place.
Old 01-12-2012, 07:33 PM   #10
UAW SKILLED TRADES
Stubbie's Avatar
continuous load
Fixed electric space heating is considered a continuous load. The branch circuit conductors and ocpd are sized at 125% of the total of the continuous loads plus any non continuous loads.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
The Following 3 Users Say Thank You to Stubbie For This Useful Post:
Furd (01-12-2012), gregzoll (01-12-2012), Speedy Petey (01-12-2012)
Old 01-12-2012, 07:36 PM   #11
continuous load
Right. There is no question of that. It's a continuous load.
Right but CB's are rated for 125% overload, correct?
-- Joe
Old 01-12-2012, 07:40 PM   #12
Average Joe/ex-Navy IC3
gregzoll's Avatar
continuous load
Hi Guys,
-- Joe
Overkill. Unless it is a pump motor, fresh air or exhaust motor that is running 24/7, you don't need to. Running your bathroom exhaust should not be on 24/7, nor is it designed for continuous use. Now of course, when determining total load, yes there is a limit that you should place on a circuit, which is clearly stated and already figured in the NEC for you.
: Now listen, Cadet. I've got a job for you. See this button?
: Don't touch it! It's the History Eraser button, you fool!
: So what'll happen?
: That's just it. We don't know. Maybe something bad, maybe something good. I guess we'll never know, 'cause you're going to guard it. You won't touch it, will you?
Old 01-12-2012, 07:43 PM   #13
gregzoll's Avatar
continuous load
-- Joe
Pick one of the manufacturers and check out what their info states. Mine state that they are rated for up to a 10kva interrupt limit, so what does that tell you.
Old 01-12-2012, 08:01 PM   #14
continuous load
What are you talking about???
The Following User Says Thank You to Speedy Petey For This Useful Post:
Old 01-12-2012, 08:14 PM   #15
Furd's Avatar
continuous load
General purpose circuit breakers should not be continuously subjected to more than 80% of their rated ampacity. There ARE some circuit breakers that are rated for continuous loads at rated ampacity.
Furd is offline   Reply With Quote
Beware of Inappropriate Load Calculation Software - Source ACCA.org JJboy HVAC 5 09-06-2011 07:25 PM
Load Calculation Fee - HVAC Contractors Please DIYerIT HVAC 2 07-30-2011 05:39 PM
Want to open up a load bearing wall - I need advice on a header to carry the load graysqwrl Building & Construction 4 07-16-2011 09:16 AM
Help 30 amp Load center for my HID lights and miscellaneous Mont@n@ Electrical 9 03-06-2010 12:49 PM
More Accurate Load Calculation zootjeff HVAC 9 12-14-2009 01:06 AM