Old 02-19-2012, 01:10 AM   #1
Rewards Points: 264
Connecting a panel box to a diesel generator
I want to connect a breaker box to a diesel generator at my cabin.
I haven't decided on a generator yet, and was hoping I could find a good set of instructions or maybe a youtube video, but don't seem to be having much luck.
Does anyone know where I could find instructions or a guide? Do I need a copper grounding rod?
tibberous is offline   Reply With Quote
Old 02-19-2012, 01:25 AM   #2
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Does the cabin have utility power also ?
Or is the cabin remote and your wanting electrical for the cabin and the generator is the sole source of power?
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 02-19-2012, 11:37 AM   #3
Generator sole power source
I hope this is not rude but I have the same question. My cabin is off grid with no other source of power and never will be. I have a Honda EU 3000 generator for my power source. I would like to run a 10/3 SOOW power cord from the 30 amp outlet on the generator hard wired to the Siemens main lug panel (G1624L1125CP). The yellow line is a #6 bare copper wire running back out of the panel and attaching to one of the pilings I've got my cabin sitting on.
AKHermit is offline   Reply With Quote
Old 02-19-2012, 01:04 PM   #4
Rewards Points: 264
Sole source.
Old 02-19-2012, 01:18 PM   #5
Yes sole source
Old 02-19-2012, 05:06 PM   #6
Idiot Emeritus
Rewards Points: 1,492
Since the gen is diesel, I'm assuming it's a bit larger than a simple pull-start one.
One thing to be aware of, a lot of these gens are 3. It's not a good idea to use two legs of a 3 gen to power a single phase panel. If the gen is 3, use a 3 panel and balance the loads.
Otherwise, just connect the gen to the panel like it's a service. The wire from the gen to the panel needs to be at least 115% of the current rating of the gen., and there needs to be a breaker somewhere to protect the wire.
A basic load calculation would give you an idea of what size of gen to get.
micromind is offline   Reply With Quote
Old 02-19-2012, 10:03 PM   #7
" Euro " electrician
frenchelectrican's Avatar
Also let me also give you a head up with triphase generatours they will come in either Delta or Wye format so that can compound the issue if you want to run in single phase therefore there is other issue will come up is the single phase rating on triphase generatour unit they will NOT be the same as triphase more like about 70% of triphase rating so that is the other thing you have to watch out on that.
If you get a triphase generator I will seriously suggest that you get a electrician assit you on the connection as I mention above.
Merci,
Marc
Mobile Home Electrical Panel Replacement rrolleston Electrical 2 01-28-2012 05:27 PM
Connecting fused knob & tube to new breaker panel carlscomputers Electrical 14 12-31-2011 11:04 AM
B&S Generator with Connecticut Electric Xfer Switch Rick5150 Electrical 19 01-20-2011 10:14 PM
Generator back feed breaker in a homeline sub panel Ward Carson Electrical 2 01-19-2011 08:13 AM
Generator sizing to match existing Panel tdnichol Electrical 4 08-25-2009 06:42 PM