Connecting Lights To 20A Circuit - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 08-28-2013, 03:51 PM   #16
In my case, all the 20A circuits in the kitchen are connected to 20A receptacle and all wiring to/from the receptacles are 12/2 cables.
I don't understand the purpose of distinguishing between a small-appliance-branch-circuit and any other branch circuit. I don't see anything wrong (or dangerous) with plugging in a "small appliance" in any receptacle regardless if it a SABC or not. For that matter, I don't see anything wrong with plugging in a light in any SABC.
rojo527 is offline   Reply With Quote
Old 08-28-2013, 04:04 PM   #17
Semi-Pro Electro-Geek
Rewards Points: 2,938
The SABC rule for kitchens exists because people are likely to use high power countertop appliances there, and they want to make sure there is adequate dedicated power available for that purpose. It's a silly rule, but a good practice.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 08-28-2013, 04:10 PM   #18
There is more to my story .. I am installing a replacement hood/fan over my stove and I connected it to an existing 20A kitchen circuit (a small-appliance-branch-circuit). An electrician asked me if the hood will have both a fan and microwave. I said no, it will have just a fan and light. He then told me that I can't hook it up to a 20A kitchen circuit. I have to hook it up to one of the 15A light circuits.
This makes absolutely no sense to me. If I install a microwave/hood I can connect it to a SABC but since it is just a fan, I can't!!
Old 08-28-2013, 04:35 PM   #19
Oso954's Avatar
Rewards Points: 1,106
If I install a microwave/hood I can connect it to a SABC...
If he said that, you need a new electrician.
I think you are assuming that. If you replied yes, he should have said that you need a 20 amp dedicated circuit for an over the range microwave.
Oso954 is online now   Reply With Quote
Old 08-28-2013, 04:52 PM   #20
Let me see if I understand you. Since there is no way of determining the load on a circuit that has receptacles, NEC is trying to say that we must provide more headroom in estimating max load for SABC vs. other branch circuits.
Old 08-28-2013, 05:11 PM   #21
I'm guessing that this is related to the restrictions on small-appliance-branch-circuits. That is, we can't have any other outlets tied to a SABC and the electrician believes that hooking up a fan/light to a SABC is not unlike hooking up a light to a SABC and therefore not allowed.
Old 08-28-2013, 08:41 PM   #22
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
You can plug a light into a SABC, but you can't hardwire a light. You can plug a counter top MW into a SABC, but not an OTR MW.
Coastal South Carolina
Old 08-29-2013, 05:55 AM   #23
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by Solarboy View Post
The breaker is sized to fit the wire and devices. If everything is wired with #12, and all the outlets are rated at 20A, ok...but if one outlet or switch is rated at 15A, either the breaker or the device has to be changed.
Not exactly, you do not need 20 amp rated switches for a 20 amp rated circuit.... switches are rated for the intended load they are to be used with.
The Following User Says Thank You to stickboy1375 For This Useful Post:
Speedy Petey (08-29-2013)
Old 08-29-2013, 06:19 PM   #24
When I started this thread, I understood my electrician to say that all lights had to be wired with #14 and I took that to mean lights cannot be connected to a 20A circuit. That is, I assumed that if I used #14 on a 20A circuit, I had to downgrade the circuit to 15A.
This thread taught me that the code violation is not about using #12 for lighting nor about hooking lights to a 20A circuit. The violation would be about connecting my kitchen lights to a small-appliance-branch-circuit.
Regarding the selection of wire gauge - my electrician also told me that I shouldn't have used #12 wire to connect an outside light to the 20A circuit in my dining room. He said that I should have used #14.
NEC does state that #14 can be used for a tap on a 20A circuit. (Ref: Table 210.24 Summary of Branch-Circuit Requirements). My electrician seems to think that this is a requirement but my interpretation is that it is "allowed", not "required". Besides saving a little money and making it easier to work with, why would anyone use #14 on a 20A circuit?
Old 08-29-2013, 06:56 PM   #25
E2 Electrician
That is incorrect... sorry.
Old 08-29-2013, 06:57 PM   #26
He is entirely incorrect. #14 wire cannot be used on a 20A circuit in that circumstance.
A tap is a very particular thing, and not just any connection to an existing circuit qualifies as a tap. In fact, almost none do. There is essentially no circumstance where you could use #14 wire as a tap from a 20A circuit in a residential setting.
It's not even allowed. The only time you'll find #14 wire on anything over a 15A breaker in a residential setting is for HVAC circuits, where very different rules apply for some very specific reasons.
The Following User Says Thank You to mpoulton For This Useful Post:
stickboy1375 (08-29-2013)
Old 08-29-2013, 06:57 PM   #27
Licensed electrician
Rewards Points: 1,608
The taps rules rarely apply, especially in residential work. The #14 on the 20 amp circuit is not allowed. Your electrician should know this.
Old 09-04-2013, 05:23 PM   #28
Thank you, everyone, for your help.
I questioned my electrician a few times about using #14 on a 20A circuit but he insisted that he knew what he was doing. He even pulled out #12 wire on a couple of 20A circuits (the wire connected to lights) and replaced it with #14. When I told him that I didn't want him to change what was already in place, his response was that since his name was on the permit, he's required to do it to his standard. I should have fired this guy awhile ago.
Old 09-04-2013, 06:32 PM   #29
????????? That doesn't make any sense. Is this being inspected? Does the inspector realize what's going on?
Old 09-04-2013, 07:29 PM   #30
The rough wiring should be ready for inspection next week. I plan on being there when the inspector comes so I can ask some key questions.
Tags
12/2 vs 14/2 , light restrictions , nec code
Circuit Breaker Arcs, Buzzs and Lights Flicker HELP! jbean8510 Electrical 5 03-05-2013 09:35 AM
Arcing between circuit breakers and flickering lights mscotter Electrical 12 07-13-2012 12:46 AM
How many outlets and lights on a circuit lowvolter Electrical 14 12-28-2011 10:14 AM
Maximum lights on a single circuit sbazzle Electrical 3 02-15-2011 08:43 AM
Should Ceiling lights be on separate circuit? handyoldgal Electrical 29 03-18-2009 08:54 PM