Connecting LB To Breaker Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 05-05-2012, 10:38 PM   #1
Connecting LB to Breaker Panel
I am bringing SE cable from meter box into a breaker panel via a 2" LB. The neck of the LB that will extend into the wall cavity is 1 1/16" long (internal depth for receiving PVC is 1 3/16"). The siding and sheathing is approximately 1" thick and there is approximately 1/4" of "dead space" between the sheathing and the back of the breaker panel. This leaves 3/16" between the end of the LB nipple and the back of the breaker panel it will be entering.
My original thoughts were to use a 2" male adapter to come into the back of the breaker panel. However, the "female/unthreaded" section of the male apapter is 1 3/8" in length (external) and 1 1/4" internal for receiving 2" conduit. So the 1 1/16" (LB neck length) + 1 3/8" (Male Adapter length) = 2 7/16". This is 1 3/16" longer than the total amount of space between the back side of the breaker panel and the back side of the 2" LB.
If I were to attempt to remove 1 3/16" from the receptacle of the male adapter, I would be removing all but 1/16" up to the internal stop so there would be practically nothing left to receive a 2" PVC stub to connect to the LB.
Would it be acceptable/recommended to remove 19/32" from both the neck of the LB and the receptacle of the male adapter and use a short PVC stub just long enough to connect the two without being exposed (roughly 19/32" + 21/32" = 1 1/4")?
If so, I could then use a nut to lock the male adapter to the breaker panel.
If there is a better way to do this, I am very much open to suggestions.
Thanks,
Ted
tedallen is offline   Reply With Quote
Old 05-06-2012, 06:49 AM   #2
Master Electrician
Rewards Points: 3,808
Thanks,
Ted
Consider using a 2" box adapter if it will work in your situation. A box adapter is a fitting with a flange that is inserted through the panel and then cemented directly into the fitting(LB) on the other side of the panel.
http://www.google.com/url?sa=t&rct=j...02wmk6fJkjFkWw
brric is offline   Reply With Quote
The Following 3 Users Say Thank You to brric For This Useful Post:
Code05 (05-06-2012), NJMarine (05-06-2012), Ravenworks (05-06-2012)
Old 05-06-2012, 07:06 AM   #3
Code05's Avatar
Rewards Points: 1,104
http://www.google.com/url?sa=t&rct=j&q=pvc%20box%20adapter&source=web&cd =5&ved=0CLoBEBYwBA&url=http%3A%2F%2Fwww.ridgelinep ipe.com%2Fliterature%2FE-344%2520Junction%2520Box-Adapter%2520Data%2520Sheet%2520(10.08).pdf&ei=omWm T8vnLMfAtweY0MiCCA&usg=AFQjCNGtp60QUl0e2jvl02wmk6f JkjFkWw
Those work great.
Code05 is offline   Reply With Quote
Old 05-06-2012, 07:48 AM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,948
WHY are you running SE cable in conduit?
The Following User Says Thank You to Speedy Petey For This Useful Post:
Jim Port (05-06-2012)
Old 05-06-2012, 11:00 AM   #5
I should have mentioned that I had a box adapter as an option. The main reason for trying to use a male adapter instead was for ease of disassembly if ever required.
Thanks,
Ted
Old 05-06-2012, 11:26 AM   #6
Maybe I am using the wrong name for it. These are two individual insulated 4/0 aluminum wires (one solid black insulator, one black with red tracer) and an unshielded aluminum for neutral coming out the side knockout of a meter enclosure and into the wall cavity via an LB.
According to the AHJ, since these conductors are not contained within a sheath (such as SEU) they must be protected by a conduit all the way into the breaker panel.
Best Regards,
Ted
breaker panel Ehren51 Electrical 3 01-20-2015 05:23 PM
Circuit Breaker Panel Height? helpless handyman Electrical 25 02-24-2014 03:06 PM
Temporarily feeding a sub panel with 10-3 30 amp breaker rrolleston Electrical 6 02-23-2012 09:40 AM
Hot water flate rate conversion to breaker panel curlycord Electrical 1 05-06-2009 07:24 PM
Outdoor breaker panel questions lhoney2 Electrical 12 07-19-2007 05:44 PM