I have a laundry room and I have 3 GFCI's I'd like to wire together. I have 12-2 going to them but can't get the outlets to work?
I have started the first one with the line(from power) to load, then then the line to the second outlet is connected to the load. Then on the second outlet. From that the former load line goes into the line, then out from the load to the third outlet which is connect to the line.
I get the LED to light on the first outlet, but have no power and the second and third outlets have no LED and no power.
Thanks in advance for your help!
Sophist is offline   Reply With Quote
Old 12-16-2008, 11:14 AM   #2
Electrical Contractor
Wire all your GFCI's on the line side.
hpp58 is offline   Reply With Quote
Old 12-16-2008, 12:21 PM   #3
Thanks! That's the one setup I haven't yet tried
Old 12-16-2008, 12:47 PM   #4
the Musigician
DangerMouse's Avatar
yup, line in, load out to next outlet line in, etc.
DM
Old 12-16-2008, 01:02 PM   #5
Rewards Points: 1,548
When the 12-2 feed serves only the GFCI protected receptacles you need only one GFCI unit sized for the amperage of the circuit.
Feed to first outlet where (let's say) the GFCI is located, connect feed to line side terminals.
Connect continuation 12-2 cable to load side of the GFCI receptacle and go to next outlet box where plain duplex receptacle is located. Continue to third box with plain duplex receptacle.
Old 12-17-2008, 08:59 AM   #6
That did the trick...Thanks a lot all of you. I really appreciate your help!
Old 12-17-2008, 07:43 PM   #7
DIYer
I've never seen anyone use a 20 amp GFCI just because the circuit was 20 amp.
Gigs is offline   Reply With Quote
Old 12-18-2008, 06:36 AM   #8
210.21(B)(1)
A single receptacle installed an a branch circuit shall have an ampere rating not less than of the branch circuit
Old 12-18-2008, 06:40 AM   #9
Originally Posted by hpp58 View Post
210.21(B)(1)
Have you ever seen a single receptacle gfci?
jerryh3 is offline   Reply With Quote
Old 12-18-2008, 07:13 AM   #10
http://www.passandseymour.com/litera...I_brochure.pdf
Old 12-18-2008, 02:47 PM   #11
210.21(B)(1)
I thought that 20 amp recpts. required a T slot.
Pardon my ignorance, as we rarely use 20 amp circuits for residential use,here in Canada.
Old 12-18-2008, 03:16 PM   #12
Doesn't the receptacle and switch count as two different outlets? Therefore, none of those listed would be considered a single receptacle.
Old 12-18-2008, 09:17 PM   #13
Now individual GFCI receptacle units at each of several outlets may be the way to go if the GFCI's are 15 amp and the circuit is 20 amp.
1. There are more than one of them so 15 amp receptacles can be on a 20 amp circuit.
2. 15 amp sub-branches may not be hung off a 20 amp circuit so the load terminals of these GFCI's may not be used.
Old 12-18-2008, 09:41 PM   #14
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Are you guys bored or what...... No reason to make this so complicated
OOOOPS did I say that.....
Old 12-19-2008, 07:18 AM   #15
Licensed electrician
Rewards Points: 1,892
If you read the box you will see that the 15 amps GFI's are rated for 20 amp pass-thru. It is fine to use the LOAD terminals to continue the circuit.