Ncs0816 10-16-2012 08:33 PM
The gauges are so different. Should I solder them together or twist them together and cap them
drwheels 10-16-2012 09:06 PM
If either was done you would limit yourself to a 15 amp breaker from using 14-2. 10-2 is usually on a 30 amp breaker and a fire hazard would result if 14-2 connected to it.
darren 10-16-2012 09:09 PM
It is possible to twist them together but not the easy job if you have never done it. Strip lots of copper and try bending the #10 around the #14.
joecaption 10-16-2012 09:47 PM
What is it your really trying to do?
I'd hate to see someone get hurt.
Ncs0816 10-16-2012 10:08 PM
I'm tring to run 100 feet of 10-2 to a new outlet at the end of my driveway. The existing outlet had a 14-2 and will be using for power
joecaption 10-16-2012 10:14 PM
Why 10-2? Seem a little over kill for just an outlet? What do you plan on powering?
Ncs0816 10-16-2012 10:25 PM
I'm using it. 10-2 will prevent more loss of volts. Correct?
CheapCharlie 10-17-2012 11:32 AM
Sure, but the voltage drop depends on what load you have on the circuit. At only 100 feet I don't think you'd have to worry about it.
Dave632 10-17-2012 11:50 AM
For a 100' run (200' total circuit length):
  • #14 = 0.505 ohms
  • #12 = 0.318 ohms
  • #10 = 0.200 ohms
  • (source)
Voltage drop, assuming a 15 Amp load (max for #14):
  • #14 = ~7.5 volts
  • #12 = ~4.8 volts
  • #10 = ~3.0 volts
Whether the 4.5 volt difference is worth the extra cost and trouble of using #10 is up to you.
CheapCharlie 10-17-2012 12:12 PM
Where are you from? If from Canada, the voltage drop is limited by code to 3% on a branch circuit.
jbfan 10-17-2012 12:18 PM
It is just a recommendation in the states, not a code issue.
CheapCharlie 10-17-2012 12:31 PM
That's why I posted that. Doesn't say in his profile
Ncs0816 10-17-2012 06:36 PM
  • #14 = 0.505 ohms
  • #12 = 0.318 ohms
  • #10 = 0.200 ohms
  • (source)
  • #14 = ~7.5 volts
  • #12 = ~4.8 volts
  • #10 = ~3.0 volts
Is the total length 200?
Live in virginia
stickboy1375 10-17-2012 06:38 PM
Just use wire nuts, align the ends and install wirenut.