Conduit Through Siding - Electrical - DIY Chatroom Home Improvement Forum
Old 06-22-2015, 08:56 PM   #1
Rewards Points: 32
Conduit through siding
I need to run 12-2 out to an above ground pool. The configuration is the breaker box is located on the outside wall of the garage. The interior walls of the garage are drywalled and the foundation is slab with the sill plate right on the slab. My plan is to fish down from the breaker box and exit the house 4" or so from the slab exiting through the vinyl siding. What is the correct way to junction through the siding?
I plan to use 1/2 or 3/4 rigid conduit so I only need to go 6" deep. It is very rocky here in TN and I don't expect I can easily get to the 18" needed for pvc.
Thanks in advance for any input!
lightsareout is offline   Reply With Quote
Old 06-22-2015, 09:08 PM   #2
Rewards Points: 2,350
Personally, I'd drill a hole just slightly bigger than the threaded boss of a rigid LB and screw a chase nipple into it and stick it in the hole. Silicone around it and strap it appropriately.
Be sure to use a wiring method approved for pools AND outdoor use. GFCI protect it at the breaker. I and other electricians here are reluctant to give advice on pools because so much could go wrong. Be sure you follow the code to a T and understand it.
Old 06-22-2015, 09:13 PM   #3
Rewards Points: 32
I will be pulling a permit and have an inspection. I understand the risks and want to do the job right. for a 20 amp GFCI breaker is a single pole ok? (please say yes as i only have one open slot!)
Old 06-22-2015, 09:25 PM   #4
Rewards Points: 13,458
Never OK to just sick it through the siding and count on caulking to to seal it.
Siding expands and contracts a lot and the caulking will just crack.
Should be removing some of the siding and installing a real siding block.
A blank 2 X 4 or 4 X 4 will work.
Something like this.
http://www.lowes.com/pd_89145-835-13...l+siding+block
Flush mounted siding blocks leak and are a pain to line up between the laps.
Old 06-22-2015, 09:32 PM   #5
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
if you are talking about a 120 volt circuit then yes, it is a single pole. If you are talking about a 240 volt or a 120/240 volt circuit, then it is a 2 pole breaker. The amperage rating is irrelevant when determining whether it is single pole or 2 pole.
Old 06-22-2015, 09:33 PM   #6
Rewards Points: 32
yes its just 120
Old 06-23-2015, 10:50 AM   #7
Special User
Rewards Points: 1,230
By the way, don't use 12-2 Romex. Romex or NM-B is not approved for wet locations, and buried conduit is considered a wet location. Can't use THHN, either. You need to use THWN or similar wet-rated wire.
I believe UF cable can be used in 3/4" conduit but I suspect you'll find that THWN in 1/2" conduit is far cheaper.
The above post is for entertainment purposes only. Its contents may, and probably will, lead to legal liability and damage or loss of property, life, or limb. Use at your own risk.
tylernt is offline   Reply With Quote
Old 06-23-2015, 10:50 AM   #8
Rewards Points: 32
is it code to install with a chase nipple like this?
Old 06-23-2015, 10:55 AM   #9
Rewards Points: 32
is THWN considered rigid?
Yes i saw that a better class wire is required.
Old 06-23-2015, 10:59 AM   #10
Special User
Rigid refers to the conduit around the wire. EMT (Electric Metallic Tubing) is the thin stuff used indoors, which is not what you want here. RMC (Rigid Metal Conduit) is the thick stuff rated for burial that you want.
THHN / THWN refers to the wire inside the conduit. You can get it in solid or stranded. Stranded is okay to use and is much easier to pull through conduit.
Old 06-23-2015, 11:00 AM   #11
Rewards Points: 32
Great thank you, stranded will save me some frustration!
Old 06-23-2015, 12:26 PM   #12
Licensed electrician
Rewards Points: 1,490
Type UF cvannot be used for a pool or spa. The ground needs to be insulated.
tylernt (06-23-2015)
Old 06-23-2015, 12:28 PM   #13
Rewards Points: 32
what type could i use? or will i need to run individual THWN strands?
Old 06-23-2015, 01:13 PM   #14
Oso954's Avatar
Rewards Points: 1,018
Can't use THHN, either. You need to use THWN or similar wet rated wire.
That probably is not the best choice of words.
Most, if not all, THHN sold today is rated as THWN (and may carry other wet ratings such as MTW).
You just need to read the info printed on the wire and/or the mfg spec sheet.
Oso954 is offline   Reply With Quote
The Following User Says Thank You to Oso954 For This Useful Post:
Old 06-23-2015, 02:57 PM   #15
Not unless you're using a cable of some sort. If you use THWN you'll need to have a continuous conduit system. In that case, I'd use either flex or seal tite and screw a connector into the rigid LB.
Siding right on studs? Davef_dci Carpentry 6 03-07-2013 05:31 PM
Conduit Attached to Exterior Foundation rjschwar Electrical 0 07-14-2012 02:14 PM
Siding: Cement Vs. Cedar Grumpy Remodeling 5 03-19-2005 01:07 PM
Siding: Aluminum vs. Vinyl Grumpy Remodeling 1 03-19-2005 12:55 PM
Siding: Aluminum vs. Vinyl Grumpy Remodeling 0 04-18-2004 03:35 PM